S

schoe

Hi all ran a ring circuit for someone about 6 months ago and when I carried out the insulation test my results were around 250 m ohms for l-n and slightly lower for l-e, anyway didn't think anything of it as we had just plastered all the rooms where the ring circuit went.

Returned to the same job today and thought I'd just check it while I was there, anyway instead of the results rising which I would have hoped they have actually dropped to around 150 ohms still well within the requirements but it's dropped never the less.

I investigated further and split the ring circuit at the half way point and tested each way, in doing so I got results which were higher on both legs separately then when they were together.

Connected everything back up and re tested from the consumer unit and the results had lowered to 150 ohms again,


Has anyone come across this before? I don't think it can still be damp that is cause the results to decress , could it be a problem with one of the socket fronts that is causing the lowering reading?

thanks for the help in advance

Chris
 
Had you tried keeping the test going and see if it rose steadily? in this case I would have thought it was damp in the fittings.

Someone could have poured juice over a socket the day before.
You may have had stronger batteries in your tester when you were testing today.
 
Don't you listen to all those cynical,angry electricians :rolleyes2: If you have the time and patience to check and re-check those readings,fair play to you.I have done this for years with things like Ra readings,call it research,interest or devilment,but it is these things that build up your experience and keep you keen.Remember not to let BS7671 spoil any joy to be had from the job.
 

Reply to Insulation resistance testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
567
Quick question. I am new to electrical installation so please be patient. You guys are great at answers. Re Insulation Testing. Why if I test...
Replies
12
Views
803
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
996
OLDBOY
O
Hi all, Testing question for you. I'm currently testing an existing domestic installation. The wiring is about 20-25 years old. We have rewired...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock