bigbaddave

Been to a job last week, Rcd tripping when its raining. Global IR 0.042. Tested 250v (L&N) cpc to save taken out all the lamps. TV's on walls were isolated via fused spur.

Problem located on External light therefore retested (L/N - CPC).. No test beetween (L&n was done)

I have now been told that the TV on the wall is not working as they are getting white flash and they have come to the conclusion that is me testing that has caused it.. Now if 500v (L-n) had been applied then yes fair enough..

Im struggling to see how this is the cause but they are seeking a response..
 
Your testing would not effect the TV, as the spur is a double pole switch the TV would of been isolated assuming you had switched it off.
 
Thats exactly my though.. The only assumption that was made was the spur actually worked the TV.

On the other note though.. Surley L&N - cpc by passed the load therefore another reason to why this should not be the cause
 
Was the tv actually on when you isolated, heard of cases people blagging new tvs this way. Used to happen frequently with a small firm i used to work for.
 
Unfortunately people with electronic equipment that is known to be problematic to them will always blame the poor sparky once he steps foot inside the door. Advice is to get a disclaimer signed first covering you before you carry out any work. The client may well have already been flickin'' through their electrical catalogue choosing a new top of the shop tele which they will be approaching you to contribute towards.
 
it doesnt matter what testing you did.
its up to the homeowner to prove you did the damage if he wants to claim.
and even a simple defect report from a tv repairman will cost them £50-60.
call their bluff and do nowt.
 
Please correct me if I'm wrong but:- Testing a circuit at 250V DC regardless of the fsu on/off, single or double pole would not damage the tv if testing l+N to CPC.

Dave they are trying it on mate, stand your ground on this one and dont put your hand in your pocket to pay for a new tv for them.
 
Why would this be a single pole fused spur, it's being used as a fused switch / isolator to a TV from a ring main, that would not make any sense to use a switched single pole fused spur flex outlet ?????

There is shed loads of installs i have been to that dont make any sence.. Like the shower someone had decided to spur off the ringmain..
 
Not all switched fused spur units are DP. An SP unit can be used on a tv like above and a DP unit must be used for boilers etc. Lets not assume its a DP on this telly but it still would not make a difference at 250V DC.
 
I know its common practice to use a lesser voltage, but you should be using 500v, if you turn back time use 1000v just for the luck the TV breaks hehe....
 

Reply to Insulation Testing Problems in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K
Evening all, as I’m preparing for my Inspection and Testing exam, I wonder if you might put me straight on something please? When performing a...
Replies
1
Views
3K
Did a check on a ring circuit, due to board having to remain live I did it at a socket.. Was an RCBO, had checked RCD side and all tested ok...
Replies
3
Views
1K
I've started to move over to AMD 2 forms for my CU installs, if only because the schedule is so much easier to tick and I can stop sticking labels...
Replies
4
Views
1K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock