Had a call out yesterday to a house where the rcd on a board supplying storage heaters would trip intermittently. When I arrived the rcd would not reset at all. The rcd was also the main switch for the board.
Obviously an earth/neutral fault I thought, so with all the mcbs off and the the rcd off I did an IR test between n+e, result >999.
So a faulty rcd then, contemplating a 20 mile round trip to Electrifix I did what I thought was a pointless thing and disconnected the earth from the earth bar and reset the rcd. It stayed up. Touched the earth on the earth bar and the rcd immediately tripped.
Retested at the board and again got good results.
Any thoughts? I did solve it but it had me going for a while.