came across this yesterday. called out to a park home to reported fault, RCD tripping with RFC fuse inserted. client was using socket outlet on cooker point to power fridge/freezer since night before. opened CU ( 6way wylex with 4 HRCs and 2 MCBs, 30mA standalone RCD front end). got out the trusty megger 400, IR readings on RFC of 0.1M, L-E, but, in addition, no continuity end/end on L and E. 4 years ago, he'd had an "electrician " install some extra sockets, 3 in total, spurred off RFC, every one had been fitted with no cpc sleeving, just bare cpc floating about behind sockets. first thought was possible S/C so sleeved and re-terminated all these, faults still there. now time to split RFC. guessed mid point and split. m1 leg IR >99M. other leg 0.1M. next S/O, same. next one , think i've found it. leg between 2 S/O's down. traced leg under home ( 2' cavity under, pulled it out suspecting rodent damage. IR tested loose cable-definitely low IR of 0.1M. closer inspection of cable revealed approx 6" from 1 end, L conductor broken and arcing damage burnt through cpc and char marks inside sheathing. 5m length of 2.5T/E installed, back to CU, >99M on RFC and E/E reinstated at 0.45 L, 0.46 N, 0.65 E.

just goes to show how easily you can go down a wrong path looking for the most obvious.
 
Lucky to find the actual damaged part, anywhere else most would have to write off that section of leg.
Goes to show the wiring that is installed without testing.
I used to go nuts when i see the builders hanging their coats and stuff on my first fix cables.
 
no, this was the original wiring. guess around 30 years old. 2.5mm solid . would never have failed it it had been good old 7/029. funny thing is, the client is thinking of replacing the CU soon and as all sockets are on 1 RFC, will probably remove the new cable and split into 2 radials to give circuits split between 2 RCDs.
 
think might have been stressed on installation, subject to large temperature fluctuations over the years ( the cable is clipped under the park home so subject to outside conditions) just finally gave way. no excessive loading.
 

Reply to interesting fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
242
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K
Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Replies
3
Views
1K
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
821
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock