I’d be keen to hear your thoughts on 1 of my customers problem.
Split board, TT system. Located in a village, neighbours report no problems.
Customer getting random tripping of sometimes 1, sometimes both RCCD’s. Totally random, no particular reason. I’ve tested the installation, nothing showing up out of the ordinary. Customer keeps a log of when these events occurs.
Tested both RCCB’s numerous times, nothing untoward. Replaced 1 with another known good 1, no difference. Moved some circuits around to try and find what’s tripping, and added another board with RCBO’s, fed from MCB from main board ( after main switch, before RCCB’s). These trip very occasionally.
Nw I’m starting to think that this maybe a supply fault, as sometimes the customer says the power comes back on without him resetting anything. Have known RCCBs to trip when power is restored, especially after a very small outage.
Ze is low for a TT around .14, measured many times.
Your thoughts gentlemen please.
 

DefyG

-
Esteemed
Arms
Reaction score
652
Could be DNO problem;
Got called to investigate same problem, no obvious faults within premises.
Later that night my client was witness to a 'wonderful firework display' as they called it when a pole transformer exploded and caught alight.
Tripping fault disappeared after transformer replaced! and been ok since (approx 7years ago).
 

littlespark

-
Esteemed
Arms
Reaction score
9,881
Trying the basics, here… but have you checked any appliances still plugged in?

Number of times it’s been: “yes, everything’s unplugged…” but either it’s just turned off at the wall, or there’s an old freezer in the garage
 

Reply to Interesting Problem !! in the Electrical Forum area at ElectriciansForums.net

Similar Threads

L
Please don't all kill me here but, I replaced 3 lights tested those 3 and all working. Went to do a 4th a restored power and now the rcd trips. Put everything back to how it was and no power to any outgoing circuits but all circuits have 240v. No tripping at all unless I put in a plug top...
Replies
17
Views
491
timhoward
timhoward
R
Hello everyone, I'm newly registered having read the boards from the shadows for a while. I have a question about neutral to earth faults and RCDs. I have read around this as much as I can but being relatively newly qualified my experience isn't as much as the collective members here so I...
Replies
24
Views
518
Roadhousezamora
R
M
Dealing with a noodle scratcher. Trying to figure out what has caused multiple GFCI outlets on separate circuits to trip at the same time. Over the last two Wednesdays in the morning something has happened which caused multiple GFCI outlets throughout the house to trip at the same time...
Replies
6
Views
700
maxrott
M
mattg4321
So there I was the other day posting on here about me going to solve faults others couldn't find and I've got one myself. It's been a while since I've been stumped but I am now. Symptoms - gate supply keeps tripping (when it's raining according to customer). There's a 6mm 3 core SWA running...
Replies
47
Views
2K
timhoward
timhoward
M
Hi all. Please be patient as I don't know much about electrics! We had a powercut in the area Tuesday 9th November afternoon - blown fuses in the sub opposite the property caused a 70 property outage. That was resolved Tuesday evening. The main switch on the RCD flipped once that evening, I...
Replies
5
Views
374
James
James

Electrical News from Electricians Forums and Friends

E
  • Article
Want to become a qualified electrician? Look carefully at the training courses on offer to avoid wasting time and money, is the advice in a new campaign from electrical industry body The Electrotechnical Skills Partnership (TESP). With thousands of searches each year on terms such as...
Replies
49
Views
6K
Marty92
Dan
  • Article
You can now link your account with social media by going to the following page. https://www.electriciansforums.net/account/connected-accounts/ We had this feature some time ago but I removed it when Facebook was found to be selling the data they collected without informing the users of what...
Replies
0
Views
2K
Dan
Dan
  • Article
There was a dodgy advert, typical clickbait, showing "how to save 90% on your electricity bill" which was not the case and it was actually showing some dangerous wiring tactics. Read the actual threads here:- What should be the code for this - C2 or C3 -...
Replies
37
Views
8K
Jurassic Sparks
Jurassic Sparks
James
  • Article
The Go Plus hot tub is being recalled because you could get electrocuted taking a dip, according to press releases from the Chartered Trading Standards Institute (CTSI). An Amazon spokesperson said: "Safety is a top priority at Amazon. "We require all products offered in our store to comply...
Replies
6
Views
3K
Dave Appleby
D
Dan
  • Article
Posted on behalf of @CKI:C.K-Tools Carl Kammerling International Ltd, also known to as ‘CKI’, are the company behind the C.K Tools brand. Founded in Germany in 1904 and with roots stretching back to 1790, we provide a wide range of hand tools, tool storage, power tool accessories and...
Replies
2
Views
4K
telectrix
telectrix

Search Forum

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Top