I’d be keen to hear your thoughts on 1 of my customers problem.
Split board, TT system. Located in a village, neighbours report no problems.
Customer getting random tripping of sometimes 1, sometimes both RCCD’s. Totally random, no particular reason. I’ve tested the installation, nothing showing up out of the ordinary. Customer keeps a log of when these events occurs.
Tested both RCCB’s numerous times, nothing untoward. Replaced 1 with another known good 1, no difference. Moved some circuits around to try and find what’s tripping, and added another board with RCBO’s, fed from MCB from main board ( after main switch, before RCCB’s). These trip very occasionally.
Nw I’m starting to think that this maybe a supply fault, as sometimes the customer says the power comes back on without him resetting anything. Have known RCCBs to trip when power is restored, especially after a very small outage.
Ze is low for a TT around .14, measured many times.
Your thoughts gentlemen please.
 
when you say you have tested the installation, have you done any checks to see if there could be a N to E fault?
 
Could be DNO problem;
Got called to investigate same problem, no obvious faults within premises.
Later that night my client was witness to a 'wonderful firework display' as they called it when a pole transformer exploded and caught alight.
Tripping fault disappeared after transformer replaced! and been ok since (approx 7years ago).
 
Trying the basics, here… but have you checked any appliances still plugged in?

Number of times it’s been: “yes, everything’s unplugged…” but either it’s just turned off at the wall, or there’s an old freezer in the garage
 

Reply to Interesting Problem !! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
575
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I had Scottish Power moving a supply this morning from one building to another so an extension could be built. I had everything ready for them...
Replies
1
Views
763
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock