Our inverter is reading about 6% higher than the PV meter.
It shows we've generated 311kwh since installed whereas the meter only reads 290.
Is this normal ?
Im guessing it's probably due to cable/efficiency losses.
 
You may find that if you're using an Owl or similar as a guide to output, this is normal as CT's aren't 100% accurate. I have various monitors attached all vary in comparison to the pulse count from the export meter. I'd suggest that you might consider the display a guide rather than an accurate output.
A display that may be more accurate is Current Cost with the Optismart.
 
Last edited by a moderator:
You may find that if you're using an Owl or similar as a guide to output, this is normal as CT's aren't 100% accurate. I have various monitors attached all vary in comparison to the pulse count from the export meter. I'd suggest that you might consider the display a guide rather than an accurate output.
A display that may be more accurate is Current Cost with the Optismart.

No, I'm comparing the inverter reading with the generation meter.
As it happens, I am using an owl to upload to pvoutput.org using pvbeancounter which has a calibration option.
I've got it set to -5% so, after a bit of trial and error, the figures on pvoutput are now the same as the generation meter.
Just wondered if a 6% difference between the inverter and the generation meter meant there was a problem somewhere but I guess it's part down to the inaccuracy of the inverter and part due to system losses.
 
Last edited by a moderator:
the difference sounds a bit high, but is probably a combination of differences in the tolerances between the meter and inverter - ie meter is reading a little high, inverter a little low, plus the cable losses.

We had a house we went back to recently a year down the line to find that the meter was actually reading higher than the inverter.
 
Just for information:-
As of this evening, my SMA inverter says: 384.4 kwh total generation since day 1.
As does PVOutput.org (no fudging of the data coming straight from the inverter, so same figs to be expected.)
And my Landis & Gyr E110 "official" generation meter says: 384.7 kwh total generation (it was showing 0.2 when first installed - which was the figure supplied on the FIT application form to British Gas.)

Incidentally, my Owl current sensing meter seems to pretty much reflect the same instantaneous Kwp values as the inverter too... but I don't archive those values, just use the portable display for convenience more than anything.

Personally, I don't think I would be too happy with a 6% discrepancy.

HTH
 
The meters used are designed for the consumption market and not the generation market. We have had meters that are 20% behind the inverter. Initially we replaced everything we could having been told that the meters are never wrong by the manufacturer. We were even primed to swap the inverter out. The only way we were able to resolve it was to swap out the meter, which then tracked the inverter.

Having had this experience we recently sent an email to all our recent customers to make sure that their meter is roughly (2-3%) in line with their inverter before we hit the peak production season. We have had one customer come back with a 20% discrepancy. Our first action will be to swap out the meter. Sadly this will require a new MCS certificate and negotiations with the fit provider....
 
This has prompted me to look in the loft.... 1.5kw system nearly a year old SAP2009 estimate 1232, Sunny Boy read 1289 and Elster reads 1316... just need to decide if I'm on a swing or roundabout now..
 
How do you recalibrate without sending back to the manufacturers?

Landis & Gyr E110 are one of the meters we use, my understanding is they are primarily used as consumption meter.
 
Last edited by a moderator:
Thanks for the replies guys.
Our meter reading is currently dead on the PV-SOL estimate we got so I don't think I'll bother getting the meter or inverter changed.
Sounds like it would be too much hassle.
Over the year, I reckon a 6% difference would only be about £60 in FIT payments anyway.
 
No, I'm comparing the inverter reading with the generation meter.
As it happens, I am using an owl to upload to pvoutput.org using pvbeancounter which has a calibration option.
I've got it set to -5% so, after a bit of trial and error, the figures on pvoutput are now the same as the generation meter.
Just wondered if a 6% difference between the inverter and the generation meter meant there was a problem somewhere but I guess it's part down to the inaccuracy of the inverter and part due to system losses.

Had a really cloudy day today and the PV meter is reading well lower than the owl so it looks like the owl is pretty inaccurate at lower wattages.
Going to try the Optismart to see if that's any better.
 
This has prompted me to look in the loft.... 1.5kw system nearly a year old SAP2009 estimate 1232, Sunny Boy read 1289 and Elster reads 1316... just need to decide if I'm on a swing or roundabout now..


We are the same the SB Inverter reads LESS than the actual Elster generation meter, so we arent going to complain :wink5:

Its out by 1.7units this year so far.....
 
The inverter will usually read less than the meter in my experience. The meters are less affected from the harmonics created by large inverters, and the meter will be OFGEM approved for a class accuracy of 2 or 1 (i.e. 1 or 2% accurate) whereas the inverter reading will be less accurate.
 
IEC 62053-21 Class 1 and Class 2 accuracy relates to the % tolerance (1% or 2%) of the base current (Ib)setting of the meter in question. Base current is typically 20A (so +/-200mA for Class 1) for most single-phase meters, but could be 5A, 10A or 15A.


As has been said, most inverters will differ in their readings from the kWh meter(s). 5-10% discrepancy is not unusual.
 
I thought the difference was due to the efficiency of the inverter and the meter reading on the inverter was calculated before the dc to ac conversion.

Tom
 
Just to update, the Optismart came yesterday and the Envir display is reading 29 watts this morning whereas the owl is reading 185 watts so confirms my thoughts that the owl is way off at lower power generations.
 
Hi, the problem I think is related to how the meter calculate the power.
I mean does it evaluate Vrms and Irms ? I know envy and Owl have the voltage set to a fixed value. This is the first problem of error. The second is, as you tell, at lower power caused also probably to the power factor that if not considered would put a big error.
 
I was concerned about a mismatch between my inverter and the generation meter. My sunnyboy remote meter agrees with the inverter and the generation meter is about 100kw behind them. This is over 10 and a bit years though (36,500 KW) so perhaps I shouldn't be worried. A 6% discrepancy sounds like something that needs looking at though.
 

Reply to Inverter reading higher kwh than meter ??? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi all , looking for some advice on my recent install of a pv and battery for my domestic property. I've noticed my smart meter readings...
Replies
0
Views
1K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
891
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
351
Hello Is it possible for solar panel monitoring to over state the actual power generated by the system? My friend’s 6.4kW system has generated...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock