Just a quick one before taking the inverter back. Recently we got an 12v to 230v inverter but started getting a shock off the casing. Tested it and around 80v but sometimes up to 120v. Is there something that can be done or is the inverter faulty
 
Is anything plugged into it when you are getting shocks.
 
You need an earth bond from battery -ve to the earth bar in fuse board.
 

Attachments

  • Inverter F653398C-66FC-4618-82B7-4B9DBB6208CA - EletriciansForums.net
    F653398C-66FC-4618-82B7-4B9DBB6208CA.jpeg
    133.9 KB · Views: 19
If you are getting shocks to earth or measuring voltage to earth from the casing of the inverter, something doesn't add up here. It says in the instructions linked by James that the earth pin of the output socket is connected to the case, so if the plug is connected to the DB and the DB is earthed, then the case should be too. The instructions may be incorrect as these cheap units are prone to rapid design changes; do a continuity check from case to DB earth of the inverter's socket, and then onwards to the earth bar in the DB.

On a similar note, is the neutral earthed within the inverter? If not, have you earthed in in the fuseboard? Not doing this won't give you shocks from the case though.
 
If you are getting shocks to earth or measuring voltage to earth from the casing of the inverter, something doesn't add up here. It says in the instructions linked by James that the earth pin of the output socket is connected to the case, so if the plug is connected to the DB and the DB is earthed, then the case should be too. The instructions may be incorrect as these cheap units are prone to rapid design changes; do a continuity check from case to DB earth of the inverter's socket, and then onwards to the earth bar in the DB.

On a similar note, is the neutral earthed within the inverter? If not, have you earthed in in the fuseboard? Not doing this won't give you shocks from the case though.
I did run a temporary earth wire from the earth in the board to the casing of inverter but this made the lights in the yard come on and off. Would this mean a fault somewhere in the installarion
 
If you are getting shocks to earth or measuring voltage to earth from the casing of the inverter, something doesn't add up here. It says in the instructions linked by James that the earth pin of the output socket is connected to the case, so if the plug is connected to the DB and the DB is earthed, then the case should be too. The instructions may be incorrect as these cheap units are prone to rapid design changes; do a continuity check from case to DB earth of the inverter's socket, and then onwards to the earth bar in the DB.

On a similar note, is the neutral earthed within the inverter? If not, have you earthed in in the fuseboard? Not doing this won't give you shocks from the case though.

Agreed,
The instructions seem to contradict themselves.

One line says for fixed applications then bat -ve must be earthed
Next line says it’s connected to the earth pin and would therefore be earthed from the board.

This is most likely some leakage from the transistors discharging through the heat sink. I would try doing as the nstructions suggest and earth the Bat -ve

The unit might not function correctly if there is a link from earth to N
 
Although, it says the case is earthed to the output but not necessarily to the DC -ve, so they might want you to connect both to earth externally which is legit. In any event, it should not be possible to get shocks between things that are tied together so something is up.

I did run a temporary earth wire from the earth in the board to the casing of inverter but this made the lights in the yard come on and off. Would this mean a fault somewhere in the installarion

Quite likely, and also likely to be the cause of the shocks. If you don't have the N-E linked, then you have an IT system in which RCDs won't work, so an earth fault on the system allied with a high-resistance rod could cause all sorts of shock hazards without tripping. Test the insulation of the installation, confirm the earthing scheme at the inverter output, etc. etc.
 
What's the earth rod at the DB for? Have you staked your inverter down too lol, the inverter I have just requires the 12v battery negative to also be linked to the inverter casing
 
What's the earth rod at the DB for? Have you staked your inverter down too lol, the inverter I have just requires the 12v battery negative to also be linked to the inverter casing
It the main earth for the yard as there is no electric up there. Just a dB. So without the earth stake there would be no earth on the installation.
[automerge]1575139531[/automerge]
You need an earth bond from battery -ve to the earth bar in fuse board.
It's not for a vehicle it's for a yard with no electric.
 
without the earth stake there would be no earth on the installation

Don't forget, the point to which fault current needs to return is not the earth your rod is in, but the neutral terminal of the inverter which is the source of supply. Earth is just another wire, which on a public supply leads to the earth mat at the substation. As your inverter does not currently have one of those, the 'wire' of mother earth leading away from your rod doesn't go anywhere so won't work. What you want the rod to do is provide a reference for the inverter output, not to earth the installation, because that you can do better with a piece of wire from MET to inverter plug.
 
Don't forget, the point to which fault current needs to return is not the earth your rod is in, but the neutral terminal of the inverter which is the source of supply. Earth is just another wire, which on a public supply leads to the earth mat at the substation. As your inverter does not currently have one of those, the 'wire' of mother earth leading away from your rod doesn't go anywhere so won't work. What you want the rod to do is provide a reference for the inverter output, not to earth the installation, because that you can do better with a piece of wire from MET to inverter plug.
So what do u suggest to do to stop the casing giving a shock
 

Reply to Inverter in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock