Currently on site and getting very confusing IR results on an EICR...any suggestions welcome!
TT @ 43.7
Ring with R1R2 values OK at around .5 as an average.
IR value consistently .049 R1R2.
Have SCOURED the place with the owner and no hidden sockets, spurs etc or neons.
Voltage is 233, so by reckoning that equates to a leak of about 0.047A. RCD ramps at 19.5 fine.
Can't see a testing fault and for sure there could well be serious rat damage, but surely with that Maths the RCD would never hold??! Confused!!!