Hi all, l recently did a eicr on a fish and chip shop.

3 phases (only one phase in use by chip shop). Earth conductor is welded together to each phase by TN-S earthing system means.

When it came to the IR test, l tested the norm tests, L-E, L-N & N-E.

Bearing in mind that we are now supposed to do the IR test without disconnecting the conductors from the CU.

All L-E readings were ok (in the hundreds Mohms).
All L-N readings were ok (same)
All of my IR tests between N-E are exactly the same on the Wylex, due to the fact that the only place l can test TO (without disconnecting conductors) is between the Neutral busbar and the earth bar.

All readings on every circuit were 0.71Mohms, which is obviously far too low.

Can l just ask where im going wrong? I normally disconnect the conductors for an accurate reading but have been told not to by other sparkys, due to regs (which im unsure of the reg this covers).

Any advice or feedback anyone???


:uhoh2::uhoh2::uhoh2::uhoh2:
 
On a periodic, you only need to test between L&N to E.

I've probably misinterpreted your post, remember, N & E are essentially connected, so N to E would be zero.
 
Whoever is telling you that your not to disconnect conductors needs a kick up the arse.

Yes you "may" do a global test across bus bars and neutral bars etc etc... But ONLY as a time saver..!
ie if you do those three tests at the CU and all is well, then job done..!! (As far as IR testing is concerned.. )

However nothing precludes you testing individual circuits. It's a very occurrence that a global IR test comes good at first bite. They nearly always need splitting down further to see where the problem child is. !

Have you read this mysterious "reg"..??
 
GN3.

Periodics, you're just testing the install is safe, ie, no Exposed parts can be live.
A L to N fault would just result in a short circuit and the breaker would trip.
 
which is silly if you think about it. if you forget to reconnect a N in the CU, then 1. that circuit will not work. 2. all the circuit cables ( except cpc) would be live. same reason that fuses in the neutral line were scrapped years ago.
 
Thanks to everyone that replied.

No Archy, l never read the reg. Its merely sparky talk between friends.

I must have mis-understood the people who have told me this or they have it wrong.

Thank you all. All feedback duly noted..
 

Reply to Ir test on bs 3036 wylex board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
605
So I’m an apprentice and I’m just trying to get a better understanding of the science behind this because the electricians who have said it have...
Replies
12
Views
1K
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
710
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
636
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
553

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock