Hi all, l recently did a eicr on a fish and chip shop.
3 phases (only one phase in use by chip shop). Earth conductor is welded together to each phase by TN-S earthing system means.
When it came to the IR test, l tested the norm tests, L-E, L-N & N-E.
Bearing in mind that we are now supposed to do the IR test without disconnecting the conductors from the CU.
All L-E readings were ok (in the hundreds Mohms).
All L-N readings were ok (same)
All of my IR tests between N-E are exactly the same on the Wylex, due to the fact that the only place l can test TO (without disconnecting conductors) is between the Neutral busbar and the earth bar.
All readings on every circuit were 0.71Mohms, which is obviously far too low.
Can l just ask where im going wrong? I normally disconnect the conductors for an accurate reading but have been told not to by other sparkys, due to regs (which im unsure of the reg this covers).
Any advice or feedback anyone???
:uhoh2::uhoh2::uhoh2::uhoh2:
3 phases (only one phase in use by chip shop). Earth conductor is welded together to each phase by TN-S earthing system means.
When it came to the IR test, l tested the norm tests, L-E, L-N & N-E.
Bearing in mind that we are now supposed to do the IR test without disconnecting the conductors from the CU.
All L-E readings were ok (in the hundreds Mohms).
All L-N readings were ok (same)
All of my IR tests between N-E are exactly the same on the Wylex, due to the fact that the only place l can test TO (without disconnecting conductors) is between the Neutral busbar and the earth bar.
All readings on every circuit were 0.71Mohms, which is obviously far too low.
Can l just ask where im going wrong? I normally disconnect the conductors for an accurate reading but have been told not to by other sparkys, due to regs (which im unsure of the reg this covers).
Any advice or feedback anyone???