When i test 1 of the rings in a domestic fit i have carried out the IR test on the L+CPC i get >299 Mohms which is expected so i then moved on to the L+N and got 288 M ohms when i connect the L to L and N to N but out of curiosity i reversed the leads on the test kit and i got < 1 M ohm which doesn't make sense.
R1 = 0.24 OHMS
R2 = 0.29 OHMS
Rn = 0.24 OHMS

Test instrument is ETHOS 7290
 
Your post is confusing me slightly. Are you saying that you are carrying out IR tests on end to end conductors on the ring (r1, rn & r2)? Or are the leads identified as L & N?

The readings you have put are in Ohms, and they look as expected.
 
Last edited:
or you are putting the two Ls in one croc and 2 Ns in the other and getting 288 and when you reverse the meter terminals you get <1Mohm ?
 
Sorry if i am confusing anyone, i just thought if i include the continuity results it might help the diagnosis.
I put both phase conductors in my brown croc clip[ and both neutral in my Green corc clips then reversed the clips so greeen onto phase and brown onto neutal. Leads wee connected correctly into the test instrument
 
Well i agree it doesn't make any sense, either your meter, or leads, are dodgy or you did something you didn't realise- are the only things i can think of. Did you repeat it and get the same thing?

Is the ring in 2.5/1.5 mm if so your r2 is surprisingly low.
 
Last edited by a moderator:
2.5mm as yes i did repeat but thanks for the ideas. I did check the other ring and repeated the same i.e swapped the leads and the results were fine so the tester is good.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Ir test
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
ceejay,
Last reply from
ceejay,
Replies
5
Views
1,702

Advert

Back
Top