benhurr

DIY
Reaction score
10
Hello to all.
I know now that 1mm T&E would be better for lights, but legally is 0.75mm Flex in conduit behind tiles and tile backer sufficient for led lights (6w) or Extractor Fan (4w)?
1 out of 3 quoting electricians said that those need to be replaced. Is it really that bad? Looking at the specs it is more than sufficient (0.75mm handles 6amp 1380 Watt) and not being exposed to movement and covered by conduit etc.
 
1 out of 3 quoting electricians said that those need to be replaced.

Did they say why? Quote a reg number?

0.75mm handles 6amp

Depends on what the data sheet says. It may be 6A when installed in free air. What about the derating factors for conduit?
Any ferrules used?
 
RCDs don't provide overcurrent protection, this will be provided by a fuse or MCB. Unless it is an RCBO where it is provided by the overcurrent portion of the RCBO.
yes fuse is possible , fused spur maybe. Light and fan is on different circuits. Fused spur for fan definitely (not for light)
 
Last edited:
How much of this project has been installed?
 
How much of this project has been installed?
this cable will only serve 1 light , the rest of the circuit is on TE cable. this room 4 led lights in total. Together with the rest of the light circuit it will be about 12 lights (including). Fan is on outlet circuit.
 
Last edited:
How much of this project has been installed?
at this moment only spare cable for fan and one short cable for mirror light are installed because those are under tiles .this cable will only serve 1 light , the rest of the circuit is on TE cable. this room 4 led lights in total. Together with the rest of the light circuit it will be about 12 lights (including). Fan is on outlet circuit.
 
It would not be compliant with the wiring regulations, the minimum size conductor for lighting circuits is 1mm^2

If there is a fused connection unit, or plug with a suitable fuse for the flex then it would comply.

The principle is that fixed wiring is protected by the mcbs or rcbos or fuses in the consumer unit and must provide disconnection times generally of 0.4s in the case of a fault.

Flex doesn't have to do this as it's usually associated with an appliance or so on, so it must have it's local fuses, and shouldn't really be used as fixed wiring, although there isn't a specific regulation preventing it.
 
It would not be compliant with the wiring regulations, the minimum size conductor for lighting circuits is 1mm^2

If there is a fused connection unit, or plug with a suitable fuse for the flex then it would comply.

The principle is that fixed wiring is protected by the mcbs or rcbos or fuses in the consumer unit and must provide disconnection times generally of 0.4s in the case of a fault.

Flex doesn't have to do this as it's usually associated with an appliance or so on, so it must have it's local fuses, and shouldn't really be used as fixed wiring, although there isn't a specific regulation preventing it.
So to recap adding fused unit like a maintenance switch will not make it compliant? Even Just for short 1m leg of wiring?
 
Fused connection unit.

What is a maintenance switch?
Fused spur switch ?

I think here is the answer suggestion that 0.75 on lighting is acceptable .75mm flex used from junction box to downlights - https://www.electriciansforums.net/threads/75mm-flex-used-from-junction-box-to-downlights.171264/
or maybe they are referring to an older regulations.
I can see now the reg It is clearly saying 1mm for lighting circuits 220v :( regardless of flexing.
But how about this way:
We remove the led driver from light fitting and place it in a box outside the room, this way it is going to be low voltage going via 0.75mm with is within current regulations.
The wire is less than a meter long.

To be honest it doesn't make much sense if this flex 0.75mm allowed on flexible applications like hanging lights but not good inside the wall in conduit behind tiles and backing board (even if it will be very short part of it)
 
Last edited:
If it's in conduit the electrician can just use the bit of flex to pull through whatever cable they feel is required.

We can all give you our own opinions on what is/is not acceptable but ultimately it is down to the electrician who does the work and signs it off to make the decision and put their name to it.

A lot of electricians are likely to refuse to connect or sign off a cable which the customer has installed themselves regardless of what size or type it is.
 
But how about this way:
We remove the led driver from light fitting and place it in a box outside the room, this way it is going to be low voltage going via 0.75mm with is within current regulations.
If it's in conduit the electrician can just use the bit of flex to pull through whatever cable they feel is required.

We can all give you our own opinions on what is/is not acceptable but ultimately it is down to the electrician who does the work and signs it off to make the decision and put their name to it.

A lot of electricians are likely to refuse to connect or sign off a cable which the customer has installed themselves regardless of what size or type it is.
 

Reply to Is 0.75mm Flex in conduit behind tiles and tile backer sufficient for led lights (6w) or Fan (4w)? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock