My work mate is installing a three phase supply to a detached steel building used for charging bikes/scooters. He has used 16mm 4 core SWA, with 80a switch fuse, am I right in saying the armouring wants earthing at the supply side but then an earth rod at the detached building, (it is PME at the origin). If so then how do you NOT earth the other end of the SWA that goes into the TP&N panel? it's all metal! Metal glands fixed to a metal DB so the earth will be installed from the PME to the detached building.. It can't not be.. But also there will be earth rod installed, I didn't think you could combine 2 earths from different systems

Oh and is a 300ma RCD Incomer required on the DB in steel shed?

appreciate your advice
 
is the building steel gurders embeded into the ground then if it is it doesnt need a rod as the steel will be earthing its self to the ground
 
Gland the SWA into a plastic enclosure below the DB and take the cores into the DB.

If the system is TT in the shed then all circuits must be protected by an RCD.
The general approach would be to use a 100mA S type, to separate it from any 30mA requirements inside the shed.
If you believe you will have problems with 100mA then you can go up to 300mA , but you need to make sure that your EFLI is low enough to be safe.
 
It does not have girders embedded into the ground. Each outgoing circuit from the DB is protected by RCBO, any idea where the reg is that states 100ma or 300ma must be used as main switch? Will this install fall under any of the special installations or locations (part 7)?
 
How far from the existing premises is the metal building out of interest? don't take this the wrong way please, do you have a regs book? and if so again no offence, do you know how to navigate it? also why is your mate asking for your advice? is he competant to do the job? again no offence to you personally at all.
 
How far from the existing premises is the metal building out of interest? don't take this the wrong way please, do you have a regs book? and if so again no offence, do you know how to navigate it? also why is your mate asking for your advice? is he competant to do the job? again no offence to you personally at all.


Its about 15m away at a guess, you've not offended me at all, I'm pretty useless at the minute with the regs book, I'm still learning how to navigate it. The person I work with is competent, I'm just trying to learn and get a step ahead of him, I want to know the answers and regs myself and the reasons why, not just have him saying "it's right...trust me".. That doesn't help me.
 
It does not have girders embedded into the ground. Each outgoing circuit from the DB is protected by RCBO, any idea where the reg is that states 100ma or 300ma must be used as main switch? Will this install fall under any of the special installations or locations (part 7)?
If you have RCBOs for all circuits then this meets the requirements for all circuits to have protection by RCD.
If you had circuits that were not on RCBOs or RCDs then the main switch would need to be an RCD. Because a 30mA could then cause the whole board to trip out unnecessarily you would then install a 100mA (or 300mA), if you have some circuits on 30mA RCDs then to discriminate you would need a time delay device as the main switch.

If the vehicles are for use on the public roads then this would come under 722 as a special location (BS7671 AMD2 2008).
 
What's the problem with exporting PME? It's not like you're running 2.5 to a shed.
 
Last edited:
extending PME, not exporting. problem could be size of bonding conductor if required.
 
extending PME, not exporting. problem could be size of bonding conductor if required.

That's what I meant tel, bad choice of words there. Thanks.

What my point is that he has a 16mm in the SWA that can be used to extend the equipontial zone. So why not use it instead of an inferior TT?

I'm not big on this but I thought this was acceptable.
 
How far from the existing premises is the metal building out of interest? don't take this the wrong way please, do you have a regs book? and if so again no offence, do you know how to navigate it? also why is your mate asking for your advice? is he competant to do the job? again no offence to you personally at all.
You ok? Bloody polite nowadays ! What's wrong?
How was that quote?
 

Reply to Is 100ma or 300ma required? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
505
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
496

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock