Couple of observations from your external house cable pic:
1. Some muppet has used the air brick to run a cable to the inside of the building hence bridging the cavity.
2. DPC cavity tray is not obvious, hence suspicion the DPC has been bridged by re-pointing the external brickwork.
3. No weep holes evident to drain the cavity wall, assumed cavity wall as the wall is in stretcher bond so therefore a 100mm skin.
Was any of this mentioned on your survey?
Survey said no breach to DPC and no sign of rising damp internally or externally.