Fault finding today,
no continuity on a FRC turns out to be 1 complete leg of the ring is simply not there. cant run new cable in due to decor/tiled floor
I was going to split the remaining sockets into 2 radials which would mean 1 radial with 3 sockets and 1 radial with only 1 socket
this sound ok ? going to use 16a mcb for each and put some form of note next to CU
i would normally put 20A breakers on a radial with anything more than a single socket attached.
p.s. it is perfectly acceptable to wire a whole house or office block without a single ring final circuit.
note is not required, it is not an unusual circuit arrangement.
how about the single socket ? 16a ok
breaker is there to protect the cable, so if it were a twin socket i would use 20A if it was a single i may put 16A but probably still go for 20A just in case someone plugs an air conditioner or similar into it.
Radial circuits are standard so no need to put note on, only 4 sockets on the original RFC that is a smallest I've come across. (if read your post right)
4 sockets 2 bedrooms min number sockets required, the note was to let any one know that 2 sockets in the same room are on different radials
Its still one circuit but 2 branch
this is true, however i have never been a fan of it as it can lead to confusion later when people assume it is a ring.
If it is not a problem for space in DB, for the sake of £6 breaker, i would put it on 2 separate circuits.
but either method would be compliant, just my personal preference.
I get that, however ring continuity should never be assumed until r1 r2 rn is confirmed
If you saw two cables into a B20 or B16 MCB, you wouldn't assume it was a ring just because there are two cables, because if you are the assuming type, you'd expect it to be on a B32 MCB. Though of course it could be ring with a lower MCB value e.g. due to cable derating.
Depending on installation method and availability of breaker, you could probably use a 25A breaker.