Hi I have just been to do a EICR just some of the points I found in 30 mins CU old with on RCD only held on wall with 1 screw
all sockets surface mounted at least one screw missing out of most no earth to any of the sockets at all on earth to the CU.
Looked like their was a earth but if their was it was in 2.5 mm and could not get any reading from it at all. One light switch with 3 core but only 2 used one still live.:banghead:
 
Last edited by a moderator:
G

Guest55

  • Thread Starter Thread Starter
  • #3
is it normal ?
well yes , and it can be worse lol.
no earthing to socket circuits ? that cant be right.
 
D

DurhamSparky

  • Thread Starter Thread Starter
  • #4
sounds like a DIY kingdom!!
 
G

Geordie Spark

  • Thread Starter Thread Starter
  • #5
Hi I have just been to do a EICR just some of the points I found in 30 mins CU old with on RCD only held on wall with 1 screw
all sockets surface mounted at least one screw missing out of most no earth to any of the sockets at all on earth to the CU.
Looked like their was a earth but if their was it was in 2.5 mm and could not get any reading from it at all. One light switch with 3 core but only 2 used one still live.:banghead:
So how was the weather in Sunderland today??
 
T

topcat

  • Thread Starter Thread Starter
  • #6
Could not get earth reading from 3 sockets on 1st floor No bonding to pipe work any or meters.
Extra sockets run all over the place Shower 8.5 kw on 6mm. extra lights and stuff run all over the place began to think it was a wind up needs complete rewire to sort if you ask me.
 
G

Guest55

  • Thread Starter Thread Starter
  • #7
Could not get earth reading from 3 sockets on 1st floor
Broken cpc then , just takes a while to trace
No bonding to pipe work any or meters. needs bonding then ?
Extra sockets run all over the place hardly unusual
Shower 8.5 kw on 6mm. sounds fine

.........needs complete rewire to sort if you ask me. not really , just a bit of time and effort to work through the defects
.....................
 
T

topcat

  • Thread Starter Thread Starter
  • #9
fair comment biff you are right they dont want me to fix the problems as they have another sparks who will do it ? Family but not part p from what was said Will need earth spike as well to get an earth as its on TT and could not get earth reading from earth cable.
 
G

Guest55

  • Thread Starter Thread Starter
  • #11
no worries , just charge the customer for the inspection and move on.
life can be alot easier when you only do the PIR's and not the remedials.
 
T

topcat

  • Thread Starter Thread Starter
  • #13
No bathroom is on ground floor so cable run is between floors.
 
S

sedgy34

  • Thread Starter Thread Starter
  • #15
Hey t c
Go to town on it, if they are not part p you will be doing the remedials or the rewire
 
SuperlecDirect - ElectriciansForums.net Electrical Suppliers
This official sponsor may provide discounts for members

Reply to Is this normal in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Aico 3000 Range
This official sponsor may provide discounts for members
uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members
Top Bottom