Hi guys could you help me please i have been given this question but i don't think it is right:

An A2 radial circuit is wired in 4mm 2 thermoplastic twin and earth cable. It is 23 meteres long. The circuit has on it 4 twin 13 amp sockets, Protection is by a 30 amp BS 3036 semi enclosed fuse, Ze for the instalation is 0.6 ohms.
socket 1 is 12 metres from the consumer unit, socket 2 is 6 metres from socket 1 and socket3 is is 2.5 metres from socket 2

Calculate the r1 & r2 value at each socket outlet
Will the protective device be suitable

could you let me know what you think the answer is so that i can compare mine

Thanks in advance
acestu
 
Given Ze= 0.6 ohms
A few assumptions here
No rating factors
4mm fte with 2.5cpc
20 c temp
R1+R2 table 9A OSG=12.02mohm/m
Thermoplastic max temp70 c table 52.1
Table41.2 max EFL zs 1.09 for BS 3036 semi enclosed
R1+R2
Sct 1 12m x12.02/1000=0.144ohm
Sct2 18m x12.02/1000=0.216ohm
Sct3 20.5m x12.02/1000=0.246ohm
Sct4 23m x12.02/1000=o.276ohm
Max R1+R2=0.276x1.20(correction factor OSG table 9c)=.3312
Zs=0.6+.3312=0.9312
Calculated Zs =0.9312
Max Zs allowable =1.09
 
Ok fellas this is what the answer says:

From table 9a in the on-site guide r1 & r2 value for the 4mm 2 / 1.5mm 2 conductors is 16.71 m ohm /M. The r1 & r2 value at the sockets is

socket 1 = 12 x 16.71 divided by 1000 = 0.2 ohms

socket 2 = 18 x 16.71 divided by 1000 = 0.3 ohms

socket 3 = 20.5 x 16.75 divided by 1000 = 0.34 ohms

Zs will be 0.34 + 0.6 = 0.94 ohms. The maximum zs for 30 amp BS 3036 fuse from table 41B1 in BS7671 (0.4s) is given as 1.14 ohms.

Using the rule of thumb for temperature correction the maximum permitted value is 1.14 x 0.75 = 0.86 ohms. This value is acceptable.


Ok so what does everybody think of th?

Please post your comments

Thanks
Acestu
 
I am only a newbie student but my thoughts first of all were the same as Mr cctbreaker ie what is the csa of the protective conductor, and then when i looked at the answer i thought what has happened to the 4th 13 amp socket surely i use the resistance reading at the end of the radial circuit in order to determine Zs, I thought i was going mad, it seems that this publication is full of mistakes because the first couple of questions seem to have errors

So just be careful if you download this E book

ie A Practical Guide To Inspection & Testing

Cheers
Acestu:confused:
 

Reply to Is this Question Right ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
626
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
753
Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
731
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
735
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock