Hi everyone,

I've come here as a DIYer asking for professional advice/opinion.

I have an 8.5KW shower on a 6mm cable and a 40amp MCB.

The shower works fine........for about 8 minutes! It invariably trips out. Sometimes it lasts 6 minutes, sometimes it lasts 10. I was considering changing the cable to 10mm (I actually changed a partial section of it to the switch) but I'm under the impression this shouldn't be necessary.

Could it be a faulty MCB or shower? It's been doing this for years and I just periodically reset the MCB.

Anyway. I've just put in a new 45a MCB hoping it will fix it. Off the finish the partial shower I got earlier!

FYI its only a short, maybe 4-5 meter run.
 
Hi everyone,

I've come here as a DIYer asking for professional advice/opinion.

I have an 8.5KW shower on a 6mm cable and a 40amp MCB.

The shower works fine........for about 8 minutes! It invariably trips out. Sometimes it lasts 6 minutes, sometimes it lasts 10. I was considering changing the cable to 10mm (I actually changed a partial section of it to the switch) but I'm under the impression this shouldn't be necessary.

Could it be a faulty MCB or shower? It's been doing this for years and I just periodically reset the MCB.

Anyway. I've just put in a new 45a MCB hoping it will fix it. Off the finish the partial shower I got earlier!

FYI its only a short, maybe 4-5 meter run.
Is it an RCD, RCBO or an MCB that is tripping? there are things to take into consideration when sizing the cable, length of cable run, installation method etc.
 
it could just be that the MCB having run close to it's rating for years has just got tired. your 45A MCB will be OK on the 6mm cable providing that said cable is not derated due to insulation.

are you sure it's MCB trip and not RCD/RCBO?
 
it could just be that the MCB having run close to it's rating for years has just got tired. your 45A MCB will be OK on the 6mm cable providing that said cable is not derated due to insulation.

are you sure it's MCB trip and not RCD/RCBO?
Agree to the question
 
I encountered the very same problem a couple of years ago and the cause turned-out to be an overheating MCB that had not been properly connected to the busbar thus creating a 'hot spot'.
 
An rcd or an rcbo has a test button and also a rating in mA. Normally 30.
An mcb does not

It's an MCB. I've attached a photo of what I fitted.

Update: I took a shower for at least 12 minutes without problem!
[automerge]1584463904[/automerge]
I encountered the very same problem a couple of years ago and the cause turned-out to be an overheating MCB that had not been properly connected to the busbar thus creating a 'hot spot'.

Well I fitted a new higher rated MCB. It didn't work at first because I didn't even attempt to tighten the busbar screw (as I say, amateur).

What you describe could have been the issue I was experiencing. I didn't want to go poking around things I know nothing about without having the part to replace.

The problem seems to now be fixed. Not bad for a 49p job. Although I should have tried your potential solution first.
[automerge]1584464152[/automerge]
it could just be that the MCB having run close to it's rating for years has just got tired. your 45A MCB will be OK on the 6mm cable providing that said cable is not derated due to insulation.

are you sure it's MCB trip and not RCD/RCBO?

Do they get tired?

The cable is clipped straight to the shower. No insulation.

So I'm all good?

Thanks ?
 

Attachments

  • 12182.jpg
    49.6 KB · Views: 29
Last edited:
It's an MCB. I've attached a photo of what I fitted.

Do they get tired?

The cable is clipped straight to the shower. No insulation.

So I'm all good?

Thanks ?
I'm sorry, but I get tired of people putting themselves in danger.
The number of times I've come across 'tired' or just loose terminals on domestic 6mm or 10mm cable joints is frightening.
You may think it's sound but IS IT??
Get someone qualified.... at least to check it.

An example of a shower 'joint', found last year.

IMG_2198.JPG
 
Well the problem was sorted quickly and painlessly and almost for free.

It's like 5 minutes a 4 screws, hardly brain surgery. The supply was isolated so who's getting the Darwin award? Do you even know who Darwin is you snarky ----?

You leave school with no GCSEs and expect me to pay you ÂŁ50 for 5 minutes to tell me a job which I know is probably better than the original install is OK? The 'qualified' person who fitted it didn't do a very good job in the first place.

I guess I'll use less pretentious forums in future.
[automerge]1584488611[/automerge]


Explain why then. Because their screwdriver has a better lubricated muffler bearing?

My question was;

Is what I've done any good/safe?

The answer from all available sources seems to be yes.

The MCB is correct, the cable is of satisfactory diameter and the shower now works without fault. So why do I need an electrician again? Oh, so I can pay them money for nothing ?
The fact that you refer to the cable size as diameter tells us all we need to know about how safe your installation is. It’s not about pretentiousness, most of us here have spent a lifetime putting right amateur lash ups in domestic installations and know the dangers of amateurs having a go. Did you torque up your new mcb to the manufacturers recommend settings, do a CPC continuity test or any of the other tests our years of experience tells us to do to qualify something as safe.
 
ÂŁ50 for five minutes , that is too cheap...

standard call-0ut is ÂŁ65
 
@Tibbyltd I hold 2 degrees one of which has a biological aspect and also involved me having to study Darwin. So yes I know quite a lot about him. What would you like to know? I also have several professional qualifications including being a full member of the IET.

I’m sorry my words touched a nerve there and upset you so much. Good news that you have resolved your issue ?
 
Well the problem was sorted quickly and painlessly and almost for free.

It's like 5 minutes a 4 screws, hardly brain surgery. The supply was isolated so who's getting the Darwin award? Do you even know who Darwin is you snarky ----?

You leave school with no GCSEs and expect me to pay you ÂŁ50 for 5 minutes to tell me a job which I know is probably better than the original install is OK? The 'qualified' person who fitted it didn't do a very good job in the first place.

I guess I'll use less pretentious forums in future.
[automerge]1584488611[/automerge]


Explain why then. Because their screwdriver has a better lubricated muffler bearing?

My question was;

Is what I've done any good/safe?

The answer from all available sources seems to be yes.

The MCB is correct, the cable is of satisfactory diameter and the shower now works without fault. So why do I need an electrician again? Oh, so I can pay them money for nothing ?
The problem wasn't sorted Tibby, you just got it working. It's easy to get electrics to work, you could have even just twisted the wires together and it would have worked but it would be dangerous. There is a 50/50 chance that the 6mm cable is not suitable for a 45A MCB and at some point the switch or MCB will overheat and possible cause a fire. I have seen so many burnt connections for showers as they have not been done properly.

I kind of get the impression though that you just want it working and are not too worried about how that is obtained. I guess if you live by yourself in a detached house you could take the risk, but if there are others living with you then you might want to check with them if they are happy to live with possible dangerous electrics.

This post really isn't designed to wind you up it's just straight talking and hoping that you will get someone to at least check it over.
 
I suggest @Tibbyltd you get an electrician in to check this circuit for piece of mind as suggested. Thread closed.
 
  • Like
Reactions: DPG
Status
Not open for further replies.

Reply to Is what I've done any good/safe? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Shower circuit (40a mcb 10mm cable 8.5kw shower ) tripping after 5 mins RESET trips after 2 mins...changed shower /cable /isolator still tripping...
Replies
7
Views
541
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
Hate these. Been called out to troubleshoot a tripping MCB. It's a house I've been to before and I know the wiring is a real dogs diner, but...
Replies
19
Views
3K
Had a real headache of a fault finding job which has left me scratching my head - RCCB on a split load board, supplying 3 circuits (shower...
Replies
20
Views
4K
Hi everyone. This has been an off and on issue for quite a few years, and seems to return for short periods of a few days or weeks and then goes...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock