Hi, i'm only a student so please forgive me for the basic question:
Say you have a generator or power transformer serving a main mccb panel, why can't the main switch of the panel be just an isolator? I've only seen the main switching device as a mccb or acb.
I know that in a house you'll have a service head and then a main isolator integral to your consumer unit, or separate. This is what I'm trying to compare with a commercial arrangement.
 
Sometimes they are used as circuit protection for the supply conductors to prevent excessive overcurrent.
 
Sometimes they are used as circuit protection for the supply conductors to prevent excessive overcurrent.
Thanks but I know that cables coming from a substation would come from the transformer's own circuit protection, acb or lv panel. Surely this would give the protection to any excessive overcurrent? It's the same with a generator, the cables are from the generator's circuit protection devices
 
True but your distribution panel could have a maximum rating of say 1000A so you install a main switch rating to provide protection for this.
 
It's also done to limit fault current.

The unit/panel will have a kA rating, without upfront protection they would have to deal with the full fault current from the transformer.
 
I'm really seeing the bigger picture, thanks.
An onsite generator or onsite transformer will be so close to the main panel that the fault current will be much higher at the panel than if the supply was coming from a remote ukpn substation
 

Reply to Isolator versus protection device on main incomer in the The Welcome Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock