I will be carrying out as part of a testing and inspection, an installation with 4 RCBO's, 2330 exam.
while carrying out an Insulation Resitance Test om the whole installation.
My question is that an RCBO can give readings as low as 2.7 Megohm N-Earth, if there are 4 will they act as being in Parallel and give an even lower result over all.
Would it be best to Test each circuit individually?

Thanks
:)
 
uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members
D

DanBrown

  • Thread Starter Thread Starter
  • #2
For me, i'd test them all seperatly.
How many circuits are you testing on the 2330 exam?,
 
G

Guest123

  • Thread Starter Thread Starter
  • #3
Hey.

Not sure you should be meggering RCBO's mate.

1. You risk damaging them.
2. As you already said they will give you a false reading.

Jusy MHO.

Cheers.
 
S

Spudnik

  • Thread Starter Thread Starter
  • #4
Not sure i would blast RCD's/RCBO's either!

As the others have said, test separate.
 
S

s1m0n

  • Thread Starter Thread Starter
  • #5
Thanks for the Advise,
I will be testing 6 circuits in all, 2 protected with a 30mA RCD, 4 with seperate RCBO's.

cheers:)
 