s1m0n

I will be carrying out as part of a testing and inspection, an installation with 4 RCBO's, 2330 exam.
while carrying out an Insulation Resitance Test om the whole installation.
My question is that an RCBO can give readings as low as 2.7 Megohm N-Earth, if there are 4 will they act as being in Parallel and give an even lower result over all.
Would it be best to Test each circuit individually?

Thanks
:)
 
Hey.

Not sure you should be meggering RCBO's mate.

1. You risk damaging them.
2. As you already said they will give you a false reading.

Jusy MHO.

Cheers.
 
Thanks for the Advise,
I will be testing 6 circuits in all, 2 protected with a 30mA RCD, 4 with seperate RCBO's.

cheers:)
 

Reply to Isulation Test with RCBO's installed in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock