When called into Pat test a factory shop floor equipment, the question was asked do Comptuers screens and printers need to be tested, If this is the case what kind of test (Class 1,2 or 3 ) apply. As we know some PC`s still have an earth conductor, so I assume it is Class 1. Please could anyone give me concrete information to show to client...Many Thanks DWEDGE
 
Wetroom Store - Network Wetroom Suppliers
This official sponsor may provide discounts for members
Advertisement - Content continues below
U

uksel

  • Thread Starter Thread Starter
  • #2
you can perform a lower voltage test if the lead is moulded in, if not you can remove the lead and test this only. my guide is down in the car but i'll have a look tomorrow for you and confirm 100% then :)

but i believe the monitor should be tested if it is CRT because of the high running internal voltages or something to that effect
 

ian.settle1

-
Mentor
Arms
When called into Pat test a factory shop floor equipment, the question was asked do Comptuers screens and printers need to be tested, If this is the case what kind of test (Class 1,2 or 3 ) apply. As we know some PC`s still have an earth conductor, so I assume it is Class 1. Please could anyone give me concrete information to show to client...Many Thanks DWEDGE

Any decent PAT tester like Seawrds or Megger have a seperate tests for IT equipment built into the program for the machine.
 
D

desertbootz

  • Thread Starter Thread Starter
  • #6
1. Having a CPC doesn't make equipment Class 1, it just means it has a cpc.

2. Class II require touch current test, not Insulation Resistence.

3. Earth Leakage current might be expected from some appliances, such a swith Mode PSU so don't bother with above if that's the case.

4. CRT can have anything up to 32kV on the flyback transformer. If that's leaking you'll know long before the PAT monkey comes around. ID the CRT PSU and then decide what test to perform. May IR, maybe Touch.

5. Visual inspection of Class II is acceptable. Test what you can (removable leads etc.)

6. All of the above may be cobblers as it's been a while since I avoided PAT testing

7. I hate PAT testing and how it's being slavishly carried out, largely by people with no more idea of what to do than they have of what it's for and before anyone flames me for that I' include myself in that statement as a former PAT monkey.

8. I got out the wrong side of bed this morning...
 
uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to IT Equipment PAT testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members
Advertisement - Content continues below
Top Bottom