Evening chaps,
I have to connect a new toilet (before anyone says it, for a client with more money than... sense/toilet roll?)
Before seeing it I presumed SFS on a RCD protected circuit, however it comes with a pre-fitted molded plug and integral 10ma rcd unit further up the factory fitted lead.
My thoughts are I could install a socket although unconventional as it is in a WC separate from the bathroom (location containing a bath or shower doesn't apply as per the regs) However this has got me thinking of the same situation if it were in the main bathroom... What would others do?
A socket is not allowed (unless some unlikely distance) so...
1) Cut the plug and wire direct to SFS (may invalidate warranty, although same as appliances if installed by a professional to SFS accepted) - This has the potential of the RCD unit built into flex being ''buried into some form of boxing by some one who gives no Shits.
2)Cut cable before RCD or get into guts to replace with one long enough to reach SFS and wire direct to SFS either 30ma or circuit 30ma protected.
3)Is there a 10ma SFS on the market?? I've had a quick look and MCB style is all I found..
Plug cut and wired to SFS is one thing, but by reducing protection from 10-30ma am I in breech of installing to manufacturers instructions?
Unusual but looking forward to hearing constructive debate, few jokes allowed!
I have to connect a new toilet (before anyone says it, for a client with more money than... sense/toilet roll?)
Before seeing it I presumed SFS on a RCD protected circuit, however it comes with a pre-fitted molded plug and integral 10ma rcd unit further up the factory fitted lead.
My thoughts are I could install a socket although unconventional as it is in a WC separate from the bathroom (location containing a bath or shower doesn't apply as per the regs) However this has got me thinking of the same situation if it were in the main bathroom... What would others do?
A socket is not allowed (unless some unlikely distance) so...
1) Cut the plug and wire direct to SFS (may invalidate warranty, although same as appliances if installed by a professional to SFS accepted) - This has the potential of the RCD unit built into flex being ''buried into some form of boxing by some one who gives no Shits.
2)Cut cable before RCD or get into guts to replace with one long enough to reach SFS and wire direct to SFS either 30ma or circuit 30ma protected.
3)Is there a 10ma SFS on the market?? I've had a quick look and MCB style is all I found..
Plug cut and wired to SFS is one thing, but by reducing protection from 10-30ma am I in breech of installing to manufacturers instructions?
Unusual but looking forward to hearing constructive debate, few jokes allowed!