Hi Guys,

Have replaced a 2-tier MK board in a restaurant today, but the 25mm tails are set solid in the wall with no hope of renewing to meter elsewhere. They are too short and I have temporally joined them with 60A connectors.

Anyone got any ideas of the best/neatest way to extend within the actual board? (just don't reach main switch).

If I was to use crimps, can you get suitable ones for 25mm, and I guess heat shrink?

What about line taps? Are these suitable?

Have thought about: Small henleys within board (too large as there are many ways being used), Soldering & stretching!

Any help guys would be appreciated.

If I use crimps, I think I may need a bigger crimper as mine only go upto 16mm. Can you get 25mm? Must be able to.

Thanks again
 
yes you can get crimps for 25mm and suitably rated!

why not connect the tails in an enclosure next to the box rather than inside the board! that way you can use lucy/henley blocks??
 
yes you can get crimps for 25mm and suitably rated!

why not connect the tails in an enclosure next to the box rather than inside the board! that way you can use lucy/henley blocks??

Hi Durham,

Thanks for the reply.

No space for any external joins, tails come straight through wall and box takes up whole enclosure, really, a work of art getting it all in. Just had a look around and see that 25mm crimps are easily getable! Just a bit of heatshrink and thats all I need? What amalmagating tape instead? Got loads in the van!

Cheers!
 
heya there m8,
yeah you can crimp 25mm2 tails and with either the heat srink or amalg tape cover the bare conductor and you are away mi old, crimped joints don't have to inspected as do soldered joint to - not like other ways of jointing ...:D
 

Reply to Joining 25mm Tails in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
Need help with a quote here. I’m wanting some sound advice. Was called out to the hot water not working so repaired the issue within the panel...
Replies
10
Views
1K
Hi guys. Im moving a consumer unit for my brother and where I was going to run a 25mm armoured through the building he has decided to put a window...
Replies
14
Views
4K
I've just finished an installation on a large outhouse around 50 meters from the main property, but I'm having issues with unusually high Zs...
Replies
11
Views
4K
Hi Guys, Came accross an install today where a new 2 way board has recently been installed to make room for a new shower circuit (Db1 - 16th...
Replies
26
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock