Was looking at a job today to quote for a rewire following a PIR (done in December) for a 3 bedroom house.

The PIR was conducted by one of Northern Ireland's biggest companies, but its nothing short of just being a bit of expensive loo roll.

Some notes on the testing:
Ze - N/A
PFC - N/A
Insulation Resistance on all circuits >299MOhms (on a 35+ year old install hmmmm).

Some of the coding's on the recommendations:
CODE 1 - Switches and sockets installed at wrong heights (they are about 1400mm to top of switch, 200mm to bottom of socket!)
CODE 1 - Cooker Outlet with combined single socket outlet (if so dangerous why are they still sold?!)
CODE 1 - Fuseboard not suitable for domestic use (its an old Wylex Rewireable board!)
CODE 1 - No rubber mats in cupboard with fuseboard (WTF!!)
CODE 1 - Kitchen lightswitch partially covered by cupboard
CODE 1 - Water Heater Switch controlled by 13A Spur Unit

It missed the shower being fed directly off the Esco's (no fusing/RCD in place), missed the exposed parts on the live esco (cover missing), and had a lot more wrong with the report than those listed, its just all I can remember from it. Absolute jokers!
 
jeez, that's not just bad, it's criminal.
 
was that a contractor or inspection and testing company?
I hope it wasn't you(noticed the location):tongue3:

No idea if a subbie did the PIR or one of the guys on the cards, but it was for one of the big boys in NI, and any spark in the country will have heard of them. NIC EIC Approved Contractors at the very least, probably ECA and JIB registered as well.
 
i was in a bit of a rush! the form looked a bit bare with no codes on it so i beefed it up a bit :) would be interested to know who it was?
 

Reply to Joke PIR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have let a flat for a several years to the same person (not a new tenancy). Hall, kitchen, bathroom, two bedrooms and lounge. All on one...
Replies
29
Views
5K
I have a customer who lives in a grand old house which suffers from damp. The ground floor sockets (2 different circuits) IR test at around...
Replies
21
Views
8K
I do seem to pick only the weirdest properties to inspect... Victorian terraced house today - with up front RCD to a Wylex fuse board and main...
Replies
24
Views
3K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
Morning, I'll preface this with the fact I have already told them I am not as yet competent to do it and they should get a trained sparky in...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock