No photo's as customer is already in dispute with kitchen fitter and was very strict about it!

I went to look at what would be involved to add a missing dishwasher point in a brand new kitchen.
House is TT. Kitchen is on a B16 radial. Hob and Cooker are on their own circuit. It's only sockets, boiler and missing dishwasher, so while not what I would have fitted, it's not an instant disaster.
Right, testing...
I found the end (to check there was a continuous cpc) and got over 3 ohms R1+R2. I then checked every connection I could find and it stayed the same. I even got the emergency Megger BR6 wheatstone bridge out of the van which is super accurate for continuity and still got the same (I was starting to seriously doubt my tester!).
Then I measured L-N PSCC and got 2.8 ohms / 82A which is getting close to not turning off instantaneously on a B16. I didn't calculate or notice volt drop, it occurred to me afterwards that this must be horrendous.

Next I took wander lead and both N and CPC are under an ohm end to end. So there must be an appalling joint on the L conductor hidden somewhere.

There's a new-ish Fusebox CU that was fitted by a guy I know so I rang him, the circuit in question was actually an immersion heater when the board was fitted. New boiler since. And no visible joint box in airing cupboard or sign of cable under the boards!

Circuit is disconnected at CU for now, and customer is going to hopefully find out from the kitchen fitter where the joint is....we'll see if they play ball. Otherwise I think this will be two new feeds and make it a ring.
 
No photo's as customer is already in dispute with kitchen fitter and was very strict about it!

I went to look at what would be involved to add a missing dishwasher point in a brand new kitchen.
House is TT. Kitchen is on a B16 radial. Hob and Cooker are on their own circuit. It's only sockets, boiler and missing dishwasher, so while not what I would have fitted, it's not an instant disaster.
Right, testing...
I found the end (to check there was a continuous cpc) and got over 3 ohms R1+R2. I then checked every connection I could find and it stayed the same. I even got the emergency Megger BR6 wheatstone bridge out of the van which is super accurate for continuity and still got the same (I was starting to seriously doubt my tester!).
Then I measured L-N PSCC and got 2.8 ohms / 82A which is getting close to not turning off instantaneously on a B16. I didn't calculate or notice volt drop, it occurred to me afterwards that this must be horrendous.

Next I took wander lead and both N and CPC are under an ohm end to end. So there must be an appalling joint on the L conductor hidden somewhere.

There's a new-ish Fusebox CU that was fitted by a guy I know so I rang him, the circuit in question was actually an immersion heater when the board was fitted. New boiler since. And no visible joint box in airing cupboard or sign of cable under the boards!

Circuit is disconnected at CU for now, and customer is going to hopefully find out from the kitchen fitter where the joint is....we'll see if they play ball. Otherwise I think this will be two new feeds and make it a ring.
Is this feeding a 20 amp switch to immersion heater.
 

Reply to Kitchen fitters..... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
242
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K
BMS installers have attended. After fitting the panel they also replaced the aged lighting in the boiler room with 6ft LED battens as instructed...
Replies
5
Views
877
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock