robmw

-
Reaction score
0
Hello. I have a new kitchen going in with a island in the middle. A 10mm t&e (protected by a 40A mcb) has been laid under kitchen floor for the hob that's going on it. No other cables can be run to it now. Trouble is I would now like two double sockets on it.

Can this be done? I thought about a mini ring from a junction box with 4mm cable. (So effectively 8mm)
 
Hello. I have a new kitchen going in with a island in the middle. A 10mm t&e (protected by a 40A mcb) has been laid under kitchen floor for the hob that's going on it. No other cables can be run to it now. Trouble is I would now like two double sockets on it.

Can this be done? I thought about a mini ring from a junction box with 4mm cable. (So effectively 8mm)


What is the 10mm feeding?
Is it not in a duct?
Why 4mm for the RFC?
 
What is the 10mm feeding?
Is it not in a duct?
Why 4mm for the RFC?

10mm feeding the kitchen hob. It is in ducting but 3 bends, tried rods. No chance.
I can't squeeze a 10mm cable in and out of a fcu for sockets. 2.5mm will not be protected by the 40A mcb at the board. That's why I thought a small two socket ring using 4mm cable from a junction box which the 10mm cable comes to before the main isolater for the hob.
 
Come off of the 10mm feed to the hob with 4mm, into a fcu and feed your 2 13Amp sockets in a Radial circuit, or have I got the wrong end of the stick? is there an RCD in this circuit.
 
Yes circuit is RCD protected. So a short piece of 4mm t&e (about 2metres) will be ok covered by a 40A mcb at board?
 
I sure you are permitted to run a short length of 2.5mm cable from the cooker switch to the FSU as that short peace of cable will only ever pull 13 amps ( because the fuse in the spur will Blow on overload ) and if there is a short to earth on the live of the 2.5mm cable the 40 amp MCB will trip before any damage is caused to the cable just make sure you can get a good connection with the 2.5mm cable and the 10mm cable in the terminal , failing that you could fit a small 2 way DB (metal of course :))
 

Reply to Kitchen island sockets in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock