Hi all I/m new to here and this is the first major installation of 3 phase and looking for advice

The unit has a incoming supply off 3 phase four wires with 2x 80amp and 1 x 100amp 1361 type 2 fuses. and used to be a truck haulage company

I am in the process of installing three, 3 phase ovens for the company which are all 14.5 kw each on a 3 phase supply.
With the other circuits the total we would be pulling would be around 82.2 kw total on balanced 3 phase.

At present we are running all but the three, 3phase ovens which are ready to be installed once confirmed.

The circuits are the following

3 x 3 phase 14.5kw ovens (to be added)
2 x 1 phase 6.5kw ovens
1 x 1 phase 9.5 kw dishwasher
1 x 3 phase 1.5kw mixer
2 x 1 phase 20amp radial circuit
1 x 1 phase 6 amp lighting circuit
1 x 1 phase CU unit of 50amp

The unit is for production of cakes therefore the ovens, dishwasher will be on most of the day.

We would be looking at adding one more oven of the same 14.5kw at a later stage.

Would the supply coming into the build need upgrading, if so which dept of the DNO would I need to contact.

Thanks
 
At the moment, assuming the 80A fuses are increased to 100A, you have 69kVA available. Since most of the load is resistive heating, the power factor will be very close to unity so you could take it as 69kW.

Your 82kW doesn't seem to include any diversity at all. I have no knowledge of bakery diversity; you could use figures for commercial kitchens generally but as the main load is the ovens, I would consult the the oven manufacturer for typical figures for normal operation. My hunch is that it will be OK even with the four ovens but you should use the best available data to calculate rather than a hunch.
 
At the moment, assuming the 80A fuses are increased to 100A, you have 69kVA available. Since most of the load is resistive heating, the power factor will be very close to unity so you could take it as 69kW.

Your 82kW doesn't seem to include any diversity at all. I have no knowledge of bakery diversity; you could use figures for commercial kitchens generally but as the main load is the ovens, I would consult the the oven manufacturer for typical figures for normal operation. My hunch is that it will be OK even with the four ovens but you should use the best available data to calculate rather than a hunch.
thanks for the quick reply. the board is follows if this helps

its a 8way 3 phase wylex board. I have arranges the following circuits to balance the load

the ovens and mixer are on 3 phase using up 4 3 phase
then on
L1 brown I have Office CU 50Amp, Lights 6amp
L2 Black Dishwasher 9.5kw, Oven 6.5kw
L3 Grey 2x 20amp radial and oven 6.5kw

Im looking for diversity for ovens (still looking)
 
At the moment, assuming the 80A fuses are increased to 100A, you have 69kVA available. Since most of the load is resistive heating, the power factor will be very close to unity so you could take it as 69kW.

Your 82kW doesn't seem to include any diversity at all. I have no knowledge of bakery diversity; you could use figures for commercial kitchens generally but as the main load is the ovens, I would consult the the oven manufacturer for typical figures for normal operation. My hunch is that it will be OK even with the four ovens but you should use the best available data to calculate rather than a hunch.
thanks again for the advice looking at the `OSG its states business premises as 100% of largest then 80% or 2nd and 60% of rest. so for the 3 phase ovens I worked this to be 34.8kw
 
Are you taking the supply rating from what's written on the DNO holders, or from the fuses themselves?
That meter is definitely only rated at 50A per phase.
no the fuses were out when we took over the unit. The fuses are 80amp x2 and the 100amp> cause they were out I replaced the old board with the new one.
 

Attachments

  • IMG_2611.jpg
    429.1 KB · Views: 17
It looks like the dno has removed the old red phase fuse holder and replaced it with a newer one, allowing the red phase (before your fuse) to feed somewhere else.

The meter is 50A so your maximum total load across all phases must be less than 50A per phase irrespective of the fuse size.

You need to contact the dno/supplier to upgrade the meter, and potentially the main supply.
 
It looks like the dno has removed the old red phase fuse holder and replaced it with a newer one, allowing the red phase (before your fuse) to feed somewhere else.

The meter is 50A so your maximum total load across all phases must be less than 50A per phase irrespective of the fuse size.

You need to contact the dno/supplier to upgrade the meter, and potentially the main supply.
thank you for your help. Ive just emailed Weston power but will call them in the morning. Thanks again
 
Yep, call WPG for 3 X 100A fuses, and then call "whoever client has contracted for an electricity bill" (NOT WPG) - for a new meter, all the new ones i have seen have been rated to 100A without CTs so you are not asking for anything special.

Good Luck
 

Reply to KVA advice in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have to install 3 x 240mm singles and 1 neutral to a panel in a LV room.the ducts aren't large enought.What happens if the singles are split...
Replies
9
Views
348
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
589
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
462
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
964
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
935

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock