Have got a new supply going in and have been told its 300KVA 3 phase now if i have worked it out correct is comes in a 433 amps which going by the size of the places i would expect to be per phase. Which i take it would be fused down to 400 amps by the DNO
 
Quick ball park sum for it is:-
3PH is Amps = Kva / 0.73
3PH Kva = Amps x 0.73

1PH Phase use 0.25 instead.
 
Last edited:
is rtrhat 2.5 th successful propportoin of the plasnts thast grow inro maturity>?
 
oooww.ps. ale is typring. bewweet shut ip. n
 
That’s based on the mythical 400V whereas a DNO transformer will be 433V and its rated current output will be based on that.

100KVA=133.3333333333333333333333333A

Not that it’ll make any odds, they’ll just bung a fuse in that’s the next size up.
 
Since when did a DNO transformer work at 433v?

For the last 80+ years.

Measure the voltage at your house. I’ll put money on it not being 230V but nearer 250V.

I assume you’ve not been an electrician for long.

Haha always has to have a dig don't you? What relevance is that. For your info I was a electrician for over 8 years before moving onto bigger and better things. :)
 
so, bigger and better things than a spark? when yo rulle the world? seig heil?
 
Haha always has to have a dig don't you? What relevance is that. For your info I was a electrician for over 8 years before moving onto bigger and better things. :)

Go on then, entertain us! What bigger and better things could their possibly be ?????
 
I await atm84’s reply with baited breath.

He’s probably be better off burger flipping, all he has to do is blithely follow the instructions on the pack. He can’t mess the chips up, I know what was done to them before they reach the outlet.


atm84, eight years in the trade and you haven’t yet worked out that 400V is a work of fiction written jointly by the EU and the IET. In the UK it is totally impractical due to the massive installed infrastructure based on 433V.
It takes but a stroke of the pen to deem 400V as the public supply voltage. The engineering side realized it’s impossible and just ignored the directive. A classic case of it’s my bat and ball, I make the rules.

Some of the lads know of my experiments of lowering the voltage on a 80,000KVA system to 400V. It ended in total disaster and I put the voltage back to 433V pronto.
 

Reply to KVA to amps help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
773
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
982
Hi all, I’m getting confused as to what the DNO are going to be installing as there main supply and as you all may be aware they tend to be a...
Replies
22
Views
4K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
519
DIYer question. I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily...
Replies
34
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock