Discuss lack of a cpc in part of a lighting circuit? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

B

brman

It is the end of the week and my brain is failing so I am hoping someone can clarify this for me.

On a periodic I found the hallway lights (two lights, two way switching) has a cpc connecting the switches and lights but it doesn't connect to the rest of the circuit. The rest of the circuit checks out fine. Lights are class 2 and switches are plastic. However the switch back boxes are metal and screws can be touched.

I initially thought a C3 as they are class 2 fittings but then thought maybe a C2 as the screws give access to the metal back box. I am sure I read something about this somewhere recently but can't find it.

Anyone care to put me right?
 
Nylon 3.5mm screws are available for the switchplates along with 30mA RCD's or RCBO's
 
It is the end of the week and my brain is failing so I am hoping someone can clarify this for me.

On a periodic I found the hallway lights (two lights, two way switching) has a cpc connecting the switches and lights but it doesn't connect to the rest of the circuit. The rest of the circuit checks out fine. Lights are class 2 and switches are plastic. However the switch back boxes are metal and screws can be touched.

I initially thought a C3 as they are class 2 fittings but then thought maybe a C2 as the screws give access to the metal back box. I am sure I read something about this somewhere recently but can't find it.

Anyone care to put me right?
the way im reading this is that part of the circuit has a cpc, but dosent go anywhere as the rest of the circuit doesnt contain an earth, or is the switches your talking about with a cpc go back to an earth?
If the cpc's are conected but dont go back to a reliable earth source then they should not be connected together as a fault on one part will liven up the other cpc's.. hmmm hope that makes some sort of sence... If all class 2 and nylon screws used then no earth requierd so c3 if an earth wire is pressent and indicated as an earth but is not earthed then c2 as this could become live in a fault situation...
 
Last edited by a moderator:
Nylon 3.5mm screws are available for the switchplates along with 30mA RCD's or RCBO's

Thanks, but it it not so much the fix that interests me (I strongly suspect if I dig in the ceiling I will find a cpc that can be connected) but what is the correct coding on a EICR?
 
code c3 if no cpc installed at all, but code c2 if it;s there but not continuous/faulty.
 
the way im reading this is that part of the circuit has a cpc, but dosent go anywhere as the rest of the circuit doesnt contain an earth, or is the switches your talking about with a cpc go back to an earth?
If the cpc's are conected but dont go back to a reliable earth source then they should not be connected together as a fault on one part will liven up the other cpc's.. hmmm hope that makes some sort of sence... If all class 2 and nylon screws used then no earth requierd so c3 if an earth wire is pressent and indicated as an earth but is not earthed then c2 as this could become live in a fault situation...

Makes sense.
The lighting circuit overall has a connected cpc. This section also has a cpc that connects the switches but it does not connect to the rest of the circuit and hence doesn't connect back to the MET. So yes, a fault to the cpc anywhere on this section would not cause ADS but will make the switch back boxes and screws live.

So a C2 as it stands but a C3 if the screws were changed to nylon as they are the only exposed conductive part?
 
nope. code C2. changing screws to nylon would not rectify the fault. you could still get a fault to back boxes, even though technically not exposed, they are still classed as an exposed conductive part.
 
nope. code C2. changing screws to nylon would not rectify the fault. you could still get a fault to back boxes, even though technically not exposed, they are still classed as an exposed conductive part.
yep as telectrix says,, if the cpc's do go back to earth then no problems, but if not then in a fault condition the non earthed cpcs will become live and so will the back boxes, so C2 if the earths are indicared as earths and conected together...
 

Reply to lack of a cpc in part of a lighting circuit? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi folks, Quick query for this still practicing regarding bill payment for a job not complete. My partner recently employed an electrician to do...
Replies
11
Views
1K
Hi, Just interested in learning what others do when faced with an old lighting installation where there is no earth and you’re installing a metal...
Replies
7
Views
2K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
552

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock