Hi everyone! :)

I've just recently moved to Laos PDR and was shocked (no pun intended) to find that the whole house has no earth wire (i.e only Live and Neutral) going to all sockets and appliances... to top it all off also no RCD's... its completely ridiculous.
I am not an electrician and have only basic knowledge of electrical stuff. But i believe I am totally unprotected in this scenario...

Now... would it be acceptable to run a seperate earth wire from each appliance say through a drilled hole in the wall to a copper earthing rod into the soil? Kind of like a TT earth but individually for each appliance? I will limit the use of anything thats not double insulated as much as I can... but a few things like the hotplate and instant shower water heater I can't avoid. An electrician actually came today and installed such an earth as I described to the shower instant water heater at least (my landlord's comment was "we normally don't use earths except for the water heaters... lol).

Anyway Id like to ask if there is anything wrong with this... I'm thinking of voltage potentials between the improvised earths and say metal pipes etc. Apart from the fact that the resistance of the copper rods would be too high to trip the MCB (at least they have those here lol)

Which brings me to the second part of my question: if I were to use those portable socket RCDs... would they work? I'm guessing it would be better than nothing, right?

Sorry for long post, thank you :)
 
Thanks for posting here. :)

That sounds bloody lethal! - I can't help you out I'm not an electrician, but I'll watch this thread because this sounds crazy!
 
Installing multiple earth rods and connections as you suggest is a bad idea. If you are going to earth it tune it all needs to be connected to the same earth, not a bunch of different ones.

My first question is whether the supply is actually earthed? If the supply neutral hasn't been reliably connected to earth at source then any earthing you add won't achieve much except a false sense of security.
 
Hi guys, yes it is completely crazy...

Well there is no way i can rewire the whole building myself... the landlord won't do it either. Why is it a bad idea to have multiple earth rods? Im not doubting you but would just like to know why? Earth loops or something like that? Surely having sone earth rods is better than none at all?

If the neutral is earthed i don't know... if i had a multimeter i could measure between one of the earth rods and neutral i guess... but i don't have one.

Regarding using portable RCDs at the sockets... also a bad or useless idea?
Cheers
 
How do you edit posts here lol

I was just thinking... in theory in this case.. wouldn't it actually be safer if the neutral was not earthed?

Because that way my body would never complete a return path for any fault current appearing on a metal chassis. Or wait... for that the whole utility electricity network would have to be floating... not just my house, right? Jeez this is doing my head in lol
I know I'm probably being a bit silly... but I'm really trying to get my head around all of this.

Edit: found the edit button haha.


Just thought about the multiple earth rod issue a bit more... say I put 3 individual ones into the ground, 1 each for water heater, washing machine and hot plate for example... Each rod will probably have a different loop resistance to ground (Ra, right?). So if the hotplate has a fault it could actually energize the chassis of the remaining two appliances, is that (part of) the problem with my suggestion?
 
Last edited:
Hi mate,

Yeah I was thinking something like that too... I can only assume they earth the neutral at the distribution transformer... I'd imagine it would be an absolute pain in the arse for the power utility company (let alone the end users) if they didn't... considering the almost daily lighting storms etc. But I will try to find out for sure.

I know I'm trying to polish a turd here lol...

So I'm thinking to just use only one earth rod connecting directly to the instant water heater... so at least that is earthed by itself. Would that be OK? (And regardless of whether they neutral earth the neutral or not?)

And for everything else I'll just use some of those 30mA socket piggy-back RCD's?

Basically what I'm trying to ask is... given this ridiculous situation I have to work with... what would be the next best thing to make it at least a little bit safer? Or better to just leave it as it is?

Thanks guys :)


EDIT: OK just read a PDF of the Lao electric power technical standards... most LV distribution has the neutral not grounded... this just keeps getting better... you can't make this stuff up. :rolleyes:

So I should probably disconnect that earth rod from the water heater again?
 
Last edited:
Just incase anyone thought I'm having a laugh (I wouldn't blame you lol) I've attached a screeshot of the PDF...

Thanks so far guys. If anyone else has any more comments or can educate me more please do so :)

74796895_435312037121199_4085050438695518208_n.jpg74796895_435312037121199_4085050438695518208_n.jpg
 
I agree with Robson689, get some local advise. It looks like you have a 25kV earth return system ie one overhead line conductor which feeds one HV terminal of the transformer the other terminal is connected to a spike so normal load current flows through earth. This will give strange voltages in the ground. The LV side looks like it is an IT system. Neither of these systems are allowed to be used for public distribution in the UK.
 
I agree with Robson689, get some local advise. It looks like you have a 25kV earth return system ie one overhead line conductor which feeds one HV terminal of the transformer the other terminal is connected to a spike so normal load current flows through earth. This will give strange voltages in the ground. The LV side looks like it is an IT system. Neither of these systems are allowed to be used for public distribution in the UK.

Thanks mate, so if this is the case as you described... I'll just put everything back the way it was. I think I'm just making things worse potentially. Back to cold showers... it's actually kinda nice haha.

So on the primary side of the pole top transformer (facing the power station i guess?) there is actually current flowing through the actual soil back to the powerstation? How does that work? That return path resistance to the power station must be in the petaohms or something... o/c basically. But im probably missing something again :)

Yeah Ive contacted a proper european electrician from a friend here.
I cant be 100% sure, but based on some dodgy translating and hand gestures, the local "electrician" who fitted the earth to the water heater yesterday seemed to say that the whole house was "grounded", because there was a cable going from the brick wall into a ground rod and that everything was ok.

If you guys are interested I'll keep you updated :D
 
Last edited:
Please keep us updated - we like to see how things work out :)
 
If you go creating an earth on all outlets and appliances you better make sure the main neutral is earthed , or you will create your own personal "death trap"

I'm not sure what you mean - can you explain? There are systems that use an earthed equipotential zone that do not have an earthed neutral. Or, if the supply is floating, the RCDs might not trip to a single fault but that won't make anything more dangerous.

That return path resistance to the power station must be in the petaohms or something

It's actually pretty low. The Ra of an earth rod is mostly associated with the soil around the rod. Although soil isn't a great conductor, the cross section of the useful path to the substation over much of its distance may be measurable in square kilometres instead of square millimetres. So if both ends are equipped with a good mat, it can be in the same order as a metallic return conductor but it costs nothing. Earth return is used in sparsely populated places where it's hard to recover the cost of the line plant. Last time I saw it was in Iceland.
 
I have seen SWER in Canada between Montral and Qubec In the case of the OP it may be an idea to have a decent local earth, cross bond to produce a local eqpotential zone within the property. Check that all circuit breakers are double pole and also have RCD protection.
 
If you google 'single wire earth return' there are a couple of bits of information about it. A european electrician may struggle as neither the hv or lv systems are used in europe.
Like wise if you google IT earthing system you should find some info.

The pictures show a three phase transformer, not a SWER system.
 
Last edited:
Thanks guys,
I tried to take some photos of a transformer... i couldn't find the one that feeds my direct area... its all just cable spaghetti ontop of poles around my house. But it might give an idea.

It'll probably be difficult to make anything out from the pics but its worth a shot :)

20191021_165810.jpg 20191021_165954.jpg 20191021_165944.jpg 20191021_165757.jpg
 
and was shocked (no pun intended) to find that the whole house has no earth wire (i.e only Live and Neutral) going to all sockets and appliances.
the local "electrician" who fitted the earth to the water heater yesterday seemed to say that the whole house was "grounded

Just pick one... it is either earthed or it isn't. If you are only taking a guess at the situation, don't even think about doing any electrical work.... If you are only taking the ---- out of us you are doing a terrible job of it.

Keep us informed
 

Reply to Laos - no earths, no RCDs... advice please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
973
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
968
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock