Hi, what type/size of wire will I need for 6 36W led batten lights in my garage?
Would 2 core 0.75mm round flex wire be ok?
 
They are likely to need an earth so two core is not suitable. If you are wiring between the fittings then 0.75 is inadequate for the purpose of fixed wiring, without more details such as circuit length and the size of protective device then 1.0 T&E should be the minimum. If you are adding additional lights from the existing set-up then it is now a requirement for them to have additional 30ma rcd protection as I assume this is a dwelling.
 
They are likely to need an earth so two core is not suitable. If you are wiring between the fittings then 0.75 is inadequate for the purpose of fixed wiring, without more details such as circuit length and the size of protective device then 1.0 T&E should be the minimum. If you are adding additional lights from the existing set-up then it is now a requirement for them to have additional 30ma rcd protection as I assume this is a dwelling.
They are likely to need an earth so two core is not suitable. If you are wiring between the fittings then 0.75 is inadequate for the purpose of fixed wiring, without more details such as circuit length and the size of protective device then 1.0 T&E should be the minimum. If you are adding additional lights from the existing set-up then it is now a requirement for them to have additional 30ma rcd protection as I assume this is a dwelling.
The led batten lights only have live & neutral connections as they are double insulated & plastic, they are replacing fluorescent tubes but will be in different positions so will need new wiring.
 
0.75 two core flex is not suitable, a cpc (earth) should be provided at all points. Best way to connect is through ceiling roses wired in at least 1.0 T&E then you can use the two core from the ceiling roses.
 

Reply to Led batten wiring in the DIY Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock