Discuss length of circuit calculation - head scratching stuff! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
S
sivoodoo
Hi all,
How do I work out the length of a circuit?
I have these figures
R1+R2 = 0.40
The circuit is wired in 2.5mm/1.5mm T&E
I take it I need to know the resistance of the T&E (where do I find this?)
Could someone give me the formula or point me in the right direction
Thank you.
I got the data from here:Untitled
1.5mm = 12.10 mOhms/m
2.5mm = 7.41 mOhms/m
12.10 + 7.41 = 19.51
19.51 mOhms/1000 = 0.01951Ohms/metre
0.4 / 0.01951 = 20.5m
I think, can someone else check my maths.
Thank you all
How accurate is this measurment, some of the results I have seen dont add up?
Thank you all
Very accurate indeed
Varying readings could be a number of factors
Parallel earth paths when recording the R1+R2
Loose or bad connections at outlets
If its a ring
Spurs giving an higher reading because of the extra lenghth
Be sure that the Rn and R1 of the ring are exactly equal
Interconnections on the ring
Reply to length of circuit calculation - head scratching stuff! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net