Hi


Scenerio : a JB that feeds a couple of lights ! , (nothing else) in a small Barn Building ( storage use only ) , it is fed via a SWA 2.5mm2 from a 63A RCCB , CU via a 16A mcb ( feeding 2 double sockets ) in the main storage barn shed , there is no isolator in the small barn , I am wanting to put in a double socket along with a LED floodlight ( outside the building ) what would I need to do , the lights they obviously need a 5A protection , and would it also need a isolator in the building itself ? .


cheers


spike
 
Lighting circuits incorporating B15, B22, E14, E27 or E40 lampholders can be protected by a device not exceeding 16A. Hard wired fittings such as fluorescent fittings there is no specific requirements. In either case the size of cable to the lighting must relate to the protective device. Is the rcd at the supply end 30ma.
 
Sorry, don't know if I am having a blonde moment, but is the 2.5mm2 swa 'protected' by a 63A overcurrent device in your description?
 
Sorry, don't know if I am having a blonde moment, but is the 2.5mm2 swa 'protected' by a 63A overcurrent device in your description?

The 2.5mm is wired back to the 16A breaker.
 
Sorry, don't know if I am having a blonde moment, but is the 2.5mm2 swa 'protected' by a 63A overcurrent device in your description?

There is no 63A overcurrent device in the description, there is only a 16A overcurrent device in the description.
The 63A device is a residual current device.
 
There is no 63A overcurrent device in the description, there is only a 16A overcurrent device in the description.
The 63A device is a residual current device.

it is fed via a SWA 2.5mm2 from a 63A RCCB ,


The OP does state it's a RCCB (residual current circuit breaker) and not a RCD.
 
The OP does state it's a RCCB (residual current circuit breaker) and not a RCD.

But an RCCB is an RCD.
RCD is the general term for a device which provides residual current protection,this can be an RCCB, RCBO, SRCD, CBR and other acronyms.

An RCCB is what most people would normally, but technically incorrectly, refer to as an RCD, they provide residual current protection only.
 
You might want to edit the post @Spike1947 and remove the links. It will cause confusion.
They get put after you do a Copy/Paste from this site.
 

Reply to Light circuit from 16A Radial in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
595
Hello, I am an enthusiast amateur undertaking wiring of two outbuilding under a building notice. I am soon to be subject to a first fix inspection...
Replies
5
Views
920
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
692

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock