G

glasgospark

upgraded board to dual rcd
everything ok
that night lighting circuit breaker trips rcd stays on
i go back try putting breaker back on trips after a couple minutes , every light in house working when breaker on
tried disconnecting all outside lights etc, also still tripped with every light switch in off position ,
after numerous attempts trying different things the rcd then tripped along with the mcb , now rcd wont stay on when lighting mcb is on everything else in house is ok , i have tried a different mcb for lighting and still happens , it also stayed on for 4 hours yesterday untill ittripped that night ,

no timers on circuit or anything

any thoughts
 
so, do the same on continuity, get an idea of the resisiance. then start opening fittings and switches. could be a trapped cable or a screw into a cable.
 
Get the IR meter on the case check no issues, are all neutrals in the correct order?
I had a similar issue once turned out to be a damaged cable below a floor board IR was >5 meg but when someone stood on the floor board it caught the nail below lucky find in the end,
I would love to meet the plumber who caused it
 
so, do the same on continuity, get an idea of the resisiance. then start opening fittings and switches. could be a trapped cable or a screw into a cable.
You suggest r1r2 every point , not done that yet , firstly it was McB only and would trip after minutes now rcd and it won't stay on atall
 
check the nail. if it's been put in with the nail head at the top, can't have been a plumber. probably a wood butcher.
 
Get the IR meter on the case check no issues, are all neutrals in the correct order?
I had a similar issue once turned out to be a damaged cable below a floor board IR was >5 meg but when someone stood on the floor board it caught the nail below lucky find in the end,
I would love to meet the plumber who caused it
Funny you should mention that , when it was just the McB tripping 2 times in a row at a squeaky floorboard when stood on it tripped straight away but after that nothing now it's rcd , which made me think its worked its way through the neutral cable now causing Imbalance on circuit and not a dead short ,
 
If the MCB trips after a few minutes it is either carrying about twice the rated current or something is heating up and then causing a fault. Clamp test the circuit of it can stay on and check the load.

Once this fault has occurred several times the expanding damage has now involved the cpc and caused the RCD to trip.

Split the circuit and IR test the sections until you can narrow down the location.
 
If the MCB trips after a few minutes it is either carrying about twice the rated current or something is heating up and then causing a fault. Clamp test the circuit of it can stay on and check the load.

Once this fault has occurred several times the expanding damage has now involved the cpc and caused the RCD to trip.

Split the circuit and IR test the sections until you can narrow down the location.
It's only pulling 2.8amp full load , I took earth out the circuit also and it stayed on for 4 hours then tripped , of course not a solution but I was testing the waters
 
you really need to split the circuit down and IR test in sections. only way.
 
If the MCB tripped and the RCD stayed on then initially you had a L-N fault so as advised check the whole circuit because I think you have agrivated the situation when you were switching the MCB on.

Also what was the point of this did you hope the fault would go away ?
 
You'd be just as quick to of disconnected all lights(there can't be many if this is domestic we are talking here) on the circuit and from the DB and has been said even if it means testing from point to point you will find the fault it may be at a termination or cable damaged it's not rocket science, you may even have to replace a length of cable God forbid, but find it you must you'll get there in the ,just break the circuit down.
 
You'd be just as quick to of disconnected all lights(there can't be many if this is domestic we are talking here) on the circuit and from the DB and has been said even if it means testing from point to point you will find the fault it may be at a termination or cable damaged it's not rocket science, you may even have to replace a length of cable God forbid, but find it you must you'll get there in the ,just break the circuit down.

Had the same thing a while back, builder had put a screw through a cable when fixing a batten up for a new ceiling. Disconnected the whole circuit at the first rose, then added and IR tested as I went until the faulty leg of cable showed up. Fairly straightforward to find after that.
 
Whats with this test each bit individually malarky? Split the circuit in half find the faulty half, split the faulty half and find the faulty half of that etc etc until you isolate the fault.
 

Reply to lighting circuit problems in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Having trouble figuring this one out. House was built 5 years ago. Eaton box and breakers. Over the past 3 weeks, the bedroom breaker keeps...
Replies
8
Views
656
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
866
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock