...what was the question?
From the first post I'm counting 24 lighting points. 24*100w = 2400w / 230 = 10.43A. I'd say 1mm t+e is border line if ref method is 101 but the volt drop is very high. Best use 1.5mm t+e on a 16A breaker in my opinion.
If you are using ref method 101 as stated you can not use a 16A breaker as your 1.5mm T&E is rated at 13A.
Table 4D5 BS 7671 2008
Its the same question as a year ago but there was no answer
50w at 230v i=p/v i=50/230 i=0.28 amps
50w at 12v i=50/12 i=4.2 amps
Is this correct?
You are forgetting that you are working it out at 12 volts, if you transpose it to 240 volts (for ease of calculation then divide your 4.2 amps by 20 which comes to 0.21 amp, so 5 LV lights to 1 ampish, so why not put 20 or so lights on a circuit, calcs work out alright.
Don't forget to add in the power factor load of the transformers ;)
On a serious note, all these quotations of loads on the 1.0 don't mention that the cable should be de-rated as, being a lighting cable, it will undoubtedly be going through loft insulation, bunched with other cables, and goodness knows what else on its route, knocking the CCC down considerably. I know 'official' cable calcs often give ridiculously pessimistic results, like demanding a 10mm cable for a lighting circuit because of all the factors, but in this case 1.0 really doesn't seem enough.
It would be be interesting to do a proper calc with the given load, and all the insulation, grouping, and other factors, and real length and see what it comes up with.
and did any one mention diversity..... ive pushed circuits to limits .... forget future proofing...... will keep us in work and are quotes will be slightly cheaper
You can probably count the amount of times ALL of a circuits lights are on, within a domestic setting on one hand over the lifetime of the installation!! As far as i'm aware, 100W incandescent lamps are no longer available, and 60W lamps are soon to follow.
I'm not saying that the circuit as described by the OP is a particularly good one, but most are over assessing the actual demand load that this circuit will ever see!! Diversity is a wonderful thing, to those that know how to use it!!! lol!!
Reply to Lighting Circuit.. Surely This Isn’t Right? in the Lighting Forum area at ElectriciansForums.net
Hi There is a lighting circuit fault in a property with the downstairs lighting circuit. I have tested the voltage and there is 230v on both...
My kitchen has track lighting. It consists of three halogen light bulbs. I've had the fixture for more than 25 years with no issues. Last night...
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Hi there, I hope it's ok to post here but I have a job lot of lighting from a job and I'd like to sell them. They are all still boxed and have...
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...