So, 1970 ish flat, 16ed board fitted in 2007, MCB covering lighting circuit. Lighting circuit has 4 x 2A/5A sockets on it.

Should they be covered by RCD/RCBO?

My feeling is no and code it C3, with a recommendation to upgrade MCB to RCBO?


Thoughts please chaps.
 
I would have thought no as it was done in line with the regulations at that time. I take it it's not tt and its only lighting plugs that can fit in the sockets?
 
I would have thought no as it was done in line with the regulations at that time. I take it it's not tt and its only lighting plugs that can fit in the sockets?

It is only 2A or 5A plugs that fit in the sockets, which in a domestic environment will only be lighting. In other environments it could be any number of things on such plugs, not just lighting.
 
Yes they should be....411.3.3. But if they complied at the time of installation and are not likely to supply equipment outdoors....(clearly not) then code 3.
If you lablel them as specifically for table lamps then no code at all IMO 411.3.3 (b)

Recently I got called out to a similar install with 13a sockets instead of 2/5a's. During a dinner party they'd plugged in a 2kw fan heater....untill someone noticed the dimmer switch was on fire!
 
Usually on the either/or type codes I look at the rest of it as a whole, if it is all spot on other than being to the earlier edition I tend to be a bit more generous and code more leniently, OTHO hand if it is a pile of poo with other C2s then I code more harshly.
 
I would code the lack of RCD additional protection for the sockets as C3. I have only ever once issued a C2 for this issue in fact.
However if there is a 13A outlet in place of a 5A outlet (I think this is the case here) on this lighting circuit, then it must be a C2 surely due to the lack of co-ordination between potential current draw and rating of accessories such as light switches. The dangers are pointed out ably by wirepuller's example in post #5.
 
I would code the lack of RCD additional protection for the sockets as C3. I have only ever once issued a C2 for this issue in fact.
However if there is a 13A outlet in place of a 5A outlet (I think this is the case here) on this lighting circuit, then it must be a C2 surely due to the lack of co-ordination between potential current draw and rating of accessories such as light switches. The dangers are pointed out ably by wirepuller's example in post #5.

Yup - I didn't really mention that on the EICR as the client commented about a problem and wanted it fixing!
 
Seriously ? If having a socket which only the lamps can be plugged in to and is controlled by a lightswitch isn't enough what the hell difference is a label going to make?

Sorry, silly assumption really. I still stand by my point though that are not general use sockets and being a completely different size and shape plug counts as being restricted to a specific load.

I understand where you are coming from but the question is about codeing for lack of RCD protection to a socket outlet. I'll refer you to the reg I quoted which makes no distinction on socket type....only that the rating is 20a or less. Which means that in order not to code a 2/5a socket must either have rcd protection,or be specifically labelled. You are assuming that DIY dave will know that a 2/5a socket is only for a table lamp,thats an assumption too far.
 
IMO , these sockets still supply hand held or portable equipment so should be RCD protected , regardless of previous regs..........
 
At least it complies with the ratio of colours for a bi-coloured protective conductor! :smilielol5::mickey::cowboy:


I suppose if you're colour blind brown and blue might appear as green and yellow ......

The guy may be on to a nice earner with that invention....LOL.....:hammer:
 

Reply to Lighting circuit with 2A & 5A sockets in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Did a couple of inspections on 2 x 2 bed ground floor flood damaged flats today, only 4 circuits in each, bizarrely one socket circuit and 2...
Replies
6
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock