Head scratcher

wired external up and down wall lights with 3c &E via a switch for both sensor and switchable lights joining the loop feed through where it's not required. I've an intermittent fault that I'm struggling to identify. I'm not having any issues with the switched lights as when the loop permanent feed is disconnected from source, the switched fittings work as they should. Done the usual checks for loose connections, water ingress, damaged cables etc but cannot see anything untoward. Thought maybe one of the sensor lights could be faulty so changed both (only 2 wait sensors out of 8 fittings), but still having the issue. 6amp MCB supplying the circuit with all fittings being 10w LED downlights or 10w GU10 LED lamp. Can't be a load issue as the fault still occurs with only the minimum amount of lights switched on.
No timing as to when the circuit will trip as had them all on for around 6 hours before I left last night with nothing tripping to receive a message from the customer complaining of the lights being out when she arrived home from work!!!!
 
Because you don't say it affects both sensor and non-sensor lamps, and they have both been left powered on for 6 hours without tripping, I assume you mean that the mcb trip occurs when the non-sensor lamps are already on and then sometime later the sensor lamps turn on. I think the problem is caused by inrush current when the sensor LED lamps turn on; the 6A mcb sees the high inrush current as a short circuit and trips. Quite a common problem with LED lamps. Made worse when the non-sensor lamps are on already and then the sensor lamps turn on because of the 'peaky' current waveform of the LED drivers all adding up.

What we need to do is limit the inrush current which means introducing either a power resistor or Negative Thermal Coefficient (NTC) Thermistor in series with the sensor lamps. The question is where to put them? The NTC Thermistor would get hot (say 150C) and the power resistor warm say 50C. Could a small box be placed near each sensor light to hold the surge suppressor? Or is there any space inside the sensor lamps?
 
Because you don't say it affects both sensor and non-sensor lamps, and they have both been left powered on for 6 hours without tripping, I assume you mean that the mcb trip occurs when the non-sensor lamps are already on and then sometime later the sensor lamps turn on. I think the problem is caused by inrush current when the sensor LED lamps turn on; the 6A mcb sees the high inrush current as a short circuit and trips. Quite a common problem with LED lamps. Made worse when the non-sensor lamps are on already and then the sensor lamps turn on because of the 'peaky' current waveform of the LED drivers all adding up.

What we need to do is limit the inrush current which means introducing either a power resistor or Negative Thermal Coefficient (NTC) Thermistor in series with the sensor lamps. The question is where to put them? The NTC Thermistor would get hot (say 150C) and the power resistor warm say 50C. Could a small box be placed near each sensor light to hold the surge suppressor? Or is there any space inside the sensor lamps?

If this is indeed the problem, what about changing to a c type Mcb or even a 10A b or c type?
Obviously the circuit will have to be suitable to make that change but let’s be honest in the uk it’s rare to find a lighting circuit that can’t take a 10A C type and still comply.
 
That's the next step tbh. Just wanted to be 100% certain there wasn't anything I may be overlooking before increasing the MCB, although I'm pretty sure there's a damaged cable between 2 of the fitting be it a screw or something but the fact it's intermittent is making it difficult to trace.
 
That's the next step tbh. Just wanted to be 100% certain there wasn't anything I may be overlooking before increasing the MCB, although I'm pretty sure there's a damaged cable between 2 of the fitting be it a screw or something but the fact it's intermittent is making it difficult to trace.

Don't change the protective device to mask a damaged cable.
 

Reply to Lighting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
426
Hi folks, Quick query for this still practicing regarding bill payment for a job not complete. My partner recently employed an electrician to do...
Replies
11
Views
1K
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
559
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock