Discuss Lights not on RCD side of board in the UK Electrical Forum area at ElectriciansForums.net
Hopefully a picture is attached.
The lights in this house are not on the RCD side of the board, there is a spare way which they could slot into and be protected by the rcd.
The lights are not split up and down so no problem between a borrowed neutral between top and bottom tripping the RCD.
Just wondered what other reasons there were why these would not have been put on the RCD side of the board ?
Lights were routinely placed on the non RCD side of the board in the past, this was probably due to the fact that when lightbulbs blew they tended to take out the RCD, in a one RCD board this would have taken out the whole installation. As this is an old board this is probably the case.
Got to disagree with roly I'm afraid, blowing lamps don't take out the RCD, they take out an MCB, usually a type B MCB because of a current surge. The reason lights were not put on the RCD when that board was installed (16th edition) was that it was not a requirement, the RCD side generally only protected socket outlets. This was the accepted practice.
Usually they don't take out the RCD, but it's not guaranteed. I have had an RCD trip due to a blowing lamp before in my own house. Not sure what came into contact with what causing the imbalance.
But I would agree that it is likely to be a 16th Edition installation where providing RCD protection to lighting circuits was unheard of.
i'd be even more concerned that it's a protecrap board.
I'd be even even more concerned that the CU has been installed on an angle. The electricity is going to pool on the non RCD side.
Must just be my customers then, lamp pops, takes out the mcb which then in turn takes out the RCD. Customer then phones electrician as they have reset the mcb and the electric hasn't come back on......?
Reply to Lights not on RCD side of board in the UK Electrical Forum area at ElectriciansForums.net
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...