Greetings.

I will probably get shot down in flames for asking this but...

If you are wiring something in singles and you are getting low on 1.5mm cable but have plenty of 2.5mm cable left would it be acceptable to run your neutral in 2.5mm even if the line is 1.5mm?

The circuit is protected by a 6 Amp MCB, a standard lighting circuit.

I have had a look at the Regs number 524.2 and it states "the neutral conductor shall have a cross sectional area not less than the line conductor". Which in this case the neutral will be bigger than the line conductor so definitely not less.

I know it sounds a bit cheap skate but in this day and age we are always looking to save costs and keep the price of the job down.

Does this seem really unprofessional to you, I mean at the end of the day the reason I'm considering doing this is to save the customer money.

Thanks.
 
Its better than the other way, where the neutral has been reduced due to an original spec supplying lots of 3 phase equipment and then removed and replaced with equipment that has both 4 pole and single phase equipment installed !

Yes I know that would be applied to sub-mains and not final circuits.
 
Last edited:
Its better than the other way, where the neutral has been reduced due to an original spec supplying lots of 3 phase equipment and then removed and replaced with equipment that has both 4 pole and single phase equipment installed !

Yes I know that would be applied to sub-mains and not final circuits. unless its single phase lighting spread across 3 phases and the neutral is shared between the phases

I hope not!! Each circuit would be made up of a neutral conductor of equal size to the line conductor.

What your describing, is what the Yanks call a ''multi branch circuit'' where all the branch circuits run off a single neutral conductor that supplies all phase line conductors.
A perfect way to overload the neutral conductor, where inductive lighting loads, make up those circuits!!
 
I hope not!! Each circuit would be made up of a neutral conductor of equal size to the line conductor.

What your describing, is what the Yanks call a ''multi branch circuit'' where all the branch circuits run off a single neutral conductor that supplies all phase line conductors.
A perfect way to overload the neutral conductor, where inductive lighting loads, make up those circuits!!

Its unlikely that 3-phase lighting will suffer that much since each phase is, as said, out of phase by 6.67ms and will be able to cope.

Its standard practice to reduce the size of the neutral in this country, although needs careful design, where most of the loads are balanced
 
Harmonic currents seem to be a bigger issue in the Regs these days.

Especially on a three phase neutral.

I hear they can get quite high.
 
Last edited:
Its unlikely that 3-phase lighting will suffer that much since each phase is, as said, out of phase by 6.67ms and will be able to cope.

Its standard practice to reduce the size of the neutral in this country, although needs careful design, where most of the loads are balanced

When your taking the return currents of inductive lighting loads of any size, that single neutral conductor starts looking susceptible, add any unbalance, even more so!! Do they still allow a single neutral conductor as the sole return path across 3 phases on inductive lighting circuits in the Reg's??

Not so much used these day's, they are increasingly feeling the effects of harmonics and whatever... I never did like these reduced neutral supply cables, and never used them, except where a neutral was required, but not in the sense of load requirement. ...ie, control and monitoring circuitry etc...
 
When your taking the return currents of inductive lighting loads of any size, that single neutral conductor starts looking susceptible, add any unbalance, even more so!! Do they still allow a single neutral conductor as the sole return path across 3 phases on inductive lighting circuits in the Reg's??

Not so much used these day's, they are increasingly feeling the effects of harmonics and whatever... I never did like these reduced neutral supply cables, and never used them, except where a neutral was required, but not in the sense of load requirement. ...ie, control and monitoring circuitry etc...

I think the regs still allow single neutrals on '3-phase' lighting 559.6.2.3, but as I said requires careful design!
 
The use of those reduced neutral cables were always a bit of a folly. They are fine with conventional loads that are substantially balanced, and won't be added too in the future. But there lies the problem with them, they were extensively used willy nilly to reduce costs, with little or no forethought to future extensions, or the now common use of inverter type motor controls and the like.

Now your seeing a lot of these main and sub-main reduced neutral cables being replaced with full sized cables. I've seen some horrendous consequences where these cables have been utilised in the wrong circumstances just to save on initial installation costs.
 
The use of those reduced neutral cables were always a bit of a folly. They are fine with conventional loads that are substantially balanced, and won't be added too in the future. But there lies the problem with them, they were extensively used willy nilly to reduce costs, with little or no forethought to future extensions, or the now common use of inverter type motor controls and the like.

Now your seeing a lot of these main and sub-main reduced neutral cables being replaced with full sized cables. I've seen some horrendous consequences where these cables have been utilised in the wrong circumstances just to save on initial installation costs.

Well until the regs change, I suppose like BS3036 semi-enclosed protective devices, they will continue to be permitted in installations. Whether or not this is aimed at existing installations or for new ones remains to be seen. Personally I wouldn't be too happy with reduced sized neutrals for many high frequency switching applications.
 
Greetings.

I will probably get shot down in flames for asking this but...

If you are wiring something in singles and you are getting low on 1.5mm cable but have plenty of 2.5mm cable left would it be acceptable to run your neutral in 2.5mm even if the line is 1.5mm?

The circuit is protected by a 6 Amp MCB, a standard lighting circuit.

I have had a look at the Regs number 524.2 and it states "the neutral conductor shall have a cross sectional area not less than the line conductor". Which in this case the neutral will be bigger than the line conductor so definitely not less.

I know it sounds a bit cheap skate but in this day and age we are always looking to save costs and keep the price of the job down.

Does this seem really unprofessional to you, I mean at the end of the day the reason I'm considering doing this is to save the customer money.

Thanks.

It will help your volt drop
 
Well until the regs change, I suppose like BS3036 semi-enclosed protective devices, they will continue to be permitted in installations. Whether or not this is aimed at existing installations or for new ones remains to be seen. Personally I wouldn't be too happy with reduced sized neutrals for many high frequency switching applications.


Well to comply with the regs its not that straight forward , if you have not assessed the loads including any harmonics and that neutral is not protected then this would be a departure from BS7671.
 

Reply to Line and neutral same size? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, just want to check something. I am on a facility which has a 4 core 70mm non armoured feed from the transformer, coming into the DB at the...
Replies
4
Views
1K
Greetings, I'm a EE and have installed many electrical systems but am now dealing with my first large 3PH install on our property. I'm not...
Replies
4
Views
864
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
770
Don't come across this very often - but I've had a CU delivered for a caravan job (not static btw), and it's been supplied with a neutral...
Replies
7
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
396

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock