That would seem a normal scenario, but not sure I understand. Exactly what are you measuring and what is the issue?
just ignore me - everyone has asked the same thing - give some clarity Anthony ?
 
That would seem a normal scenario, but not sure I understand. Exactly what are you measuring and what is the issue?
just ignore me - everyone has asked the same thing - give some clarity Anthony ?
Apologies. the the RCD shares the up and down sockets. When I test the sockets on the Kewtech on the trip Le rcd, insulation etc it shows no voltage. I press test and the RCD trips. GGGrrrrrrrrrrrTRIP_2324.png
 
Last edited by a moderator:
I'm not au fait with mfts prefer separates so I can only assume it is indicating a poor earth path. The fault loop path is line to earth which the meter is looking for so if the earth is not there it may indicate 0v.
 
I think DPG meant measuring the voltage directly.

By the way I think you have the L and N leads plugged in the wrong way round on the back of the Kewtech, unless I'm reading the wrong manual ?
 
I have a similar Kewtech though mine isn't a 'plus'.
You are right, you should see the Line/Neutral voltage on the screen at that point.
From the manual:
1636805257215.png

So you are right to raise your eyebrows.
I've just noticed you said ALL upstairs sockets are like this. Are they on their own circuit or same ring as downstairs?
Have you re-proved the tester and test leads are working downstairs or elsewhere since discovering this?
I'd put the MFT down and pick up the 2 pole tester and go back to first principles, L-E and L-N tests at all sockets, maybe check wiring for circuit at CU too. Until you are seeing a normal supply at the sockets there's no point proceeding with loop tests. Logic will eventually prevail...

This is an interesting one, so do report back!
 
I have a similar Kewtech though mine isn't a 'plus'.
You are right, you should see the Line/Neutral voltage on the screen at that point.
From the manual:
View attachment 91970

So you are right to raise your eyebrows.
I've just noticed you said ALL upstairs sockets are like this. Are they on their own circuit or same ring as downstairs?
Have you re-proved the tester and test leads are working downstairs or elsewhere since discovering this?
I'd put the MFT down and pick up the 2 pole tester and go back to first principles, L-E and L-N tests at all sockets, maybe check wiring for circuit at CU too. Until you are seeing a normal supply at the sockets there's no point proceeding with loop tests. Logic will eventually prevail...

This is an interesting one, so do report back!
Hi, upstairs sockets are on a different breaker yet share the same RCD. All leads Nulled and yes will try again tomorrow and do and EICR on the fuseboard.

Thank you
 

Reply to Line carrying voltage, neutral no voltage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Replies
25
Views
1K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
471
I know the effect of a lost neutral (floating neutral) on a 3 phase system, and the theory of why the line voltages can vary. However, I have...
Replies
1
Views
731
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
549
Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Replies
1
Views
427

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock