Hi. Turned power off to change a socket front. Turned off at breaker not the RCD or mains. Checked that socket was dead got these readings Line to Neutral 0 volts , live earth 30 volts , neutral earth 30 volts. This is an old French house on a 3 phase supply Split at consumer unit and then each board of which there are 9 are using one of the phases per RCD. We had some shared neutral issues on the lighting circuits when we replaced all the boards. Why am I seeing voltage from neutral to earth and live to earth ? Any help would be appreciated.
 

pc1966

Esteemed
Arms
Reaction score
11,074
If it is French then the MCB will be double-pole, so when you switch it off both the L & N are "floating" and not connected to anything.

However, they will have some capacitance to any live cables nearby, and if you use a digital multimeter with (probably) a 10M ohm impedance to check for voltage you only need 3 microamps (0.000,003A) of coupled current to see 30V appear.

That is one reason why electrical apprentices have the it drummed in to them to use a "voltage tester" for proving dead, as they take a few milliamps (0.001A or more) to operate the LEDs. The other more important reason is voltage testers are simple, reliable, and safe. You don't have the opportunity to set them to the wrong setting and either kill yourself by the meter blowing up in your face, or killing yourself by selecting DC volts and not seeing 230V of AC volts being present.

For example:
 
OP
S
Reaction score
0
Hi. Thank you. So you’re basically saying there is no issue. By using a multimeter I’m picking up on voltage from other cables nearby ? This is not something else like a bad earth as we’re on TT systems here.
 

pc1966

Esteemed
Arms
Reaction score
11,074
Using a multimeter to check for power is frowned upon by the electrical industry due to the number of ways it can go badly wrong! Reading "phantom voltages" as you are reporting is really the least of your worries.

So if you are doing much in the way of DIY then getting a basic voltage tester is a very good idea. I prefer the sort that don't need batteries as it is one less thing to forget to change and find it has leaked and ruined it. Equally you must test the tester every before using it! A professional would also buy a "proving unit" to provide various voltages on-demand to check the tester responds OK, but for DIY testing it on a known live outlet before checking something is not powered is a minimum step.

The issue of how good the earth rod is in a TT system is harder to check. A professional electrician would have equipment to measure that, most simply using a "multi function tester" (MFT) that can measure the earth fault impedance, but they cost around the £500-1000 region typically so not many DIYers are going to have access to one.

In the UK you can get better socket testers that do report high fault impedance, but they are not really designed for TT use as the majority of the UK is on TN-S or TN-C-S that has (or should have!) a very low and reliable earth impedance. For example:

I don't know if a similar product is available in France to do that job with thresholds that are appropriate for TT installations, but maybe @Mike Johnson will know as he has some experience of French electrical work.
 
Last edited:

Mike Johnson

-
Esteemed
Reaction score
4,092
I think the problem you are seeing is the three phase board having three RCD's one for each phase, only turning off one RCD on one phase will not fully isolate any leakage from the other phase's the only way to fully isolate the board is at the Tetrapolaire Disjoncteur de Branchement i.e. the EDF main switch, the one that goes off if you try to draw too munch power.

The socket testers are very good, but I have never seen a French one, you can use a UK version, but the only way is with a EU/UK extension lead correctly wired, don't be tempted to buy a UK version and use it in a EU/UK convertor most convertors reverse the polarity and will give false readings
 

Mike Johnson

-
Esteemed
Reaction score
4,092
Don't you just love predictive text, just noticed on the above post you may de drawing "munch" power.

Should have mentioned the fact that even with the whole thing switched off the CPC is still connected to the earth bar in the CU together with all the other circuits and you would be getting into the realms of parallel paths and possibly picking up potential earth voltage through the spike, open the cut off bar, (Barre de coupure), but do be careful when doing this as none of the circuits will be protected whilst it is disconnected, so mains off first then disconnect the earth bar.
 
OP
S
Reaction score
0
Hi. Thanks to you all for your help. I do have a socket tester but it only checks polarity and it will do an RCD trip test. I understand what you’re saying about if I isolate 1 RCD on one of the 9 boards I’m only stopping current on my particular circuit. In parallel I will have power operating in other boards on the same phase plus on the other 2. What I still don’t understand is that there is no circuit after the main EDF switch that is not RCD protected - so if I’m seeing current from earth to line then there is leakage to earth that I’m picking up from parallel paths why are the other RCDs not tripping on this ? Or is it just not enough to do it. Ie 40ma on one RCD would need to be present and if I’ve got a little leakage on all circuits and poor earthing through the spikes I’m seeing this on the multimeter ?
What would be the best idea ? MFT earth fault loop impedance tester ( I have access to one ) and test the earth spike at each board that has one and remedy the earthing situation if there is one ? I think the impedance is supposed to be no higher that 100ohms on a TT in France?
 

pc1966

Esteemed
Arms
Reaction score
11,074
What I still don’t understand is that there is no circuit after the main EDF switch that is not RCD protected - so if I’m seeing current from earth to line then there is leakage to earth that I’m picking up from parallel paths why are the other RCDs not tripping on this ? Or is it just not enough to do it.
Not enough to trip. Most RCD need 15-30mA to trip, but 30V on a 10M meter is only 0.003mA

What would be the best idea ? MFT earth fault loop impedance tester ( I have access to one ) and test the earth spike at each board that has one and remedy the earthing situation if there is one ? I think the impedance is supposed to be no higher that 100ohms on a TT in France?
If you put the MFT on to any socket and run the earth loop test it will tell you the overall impedance of supply + earth rod. Given the supply is going to be much lower than the rod it basically tells you the rod impedance.

I don't know the French regulations, but in the UK if you have 100mA or 30mA RCDs in use the rod has to be below 200 ohms to meet both the RCD limits (500 ohm & 1.67k) for 50V max rod voltage AND to be stable against seasonal variations of frost or drought, etc.

If you have something larger like a farm with a 300mA RCD then the rod should be less than 167 ohms (50V / 0.3A) and so on, but really you want it as low as practical and aiming for sub-100R is achievable with one or two 2m rods in most cases.
 
OP
S
Reaction score
0
Not enough to trip. Most RCD need 15-30mA to trip, but 30V on a 10M meter is only 0.003mA


If you put the MFT on to any socket and run the earth loop test it will tell you the overall impedance of supply + earth rod. Given the supply is going to be much lower than the rod it basically tells you the rod impedance.

I don't know the French regulations, but in the UK if you have 100mA or 30mA RCDs in use the rod has to be below 200 ohms to meet both the RCD limits (500 ohm & 1.67k) for 50V max rod voltage AND to be stable against seasonal variations of frost or drought, etc.

If you have something larger like a farm with a 300mA RCD then the rod should be less than 167 ohms (50V / 0.3A) and so on, but really you want it as low as practical and aiming for sub-100R is achievable with one or two 2m rods in most cases.
Ok. I’ll do some testing and report back. Thank you.
 

Mike Johnson

-
Esteemed
Reaction score
4,092
The EDF main switch is a 100ma S Type RCD with current control in case you try to draw more than the tariff you are paying for, the smart meters now being installed everywhere are less tolerant than the old meters and I have been told only have a head of 2% whereas the prior meters had a head of 12%, this is why many who have the meter changed think they are using more electricity and many had to increase their tariff to cope with what they where previously getting away with.

TT Earth spike needs to be below 100Ω to be compliant.

If you are going the MFT route be careful what you use as some of them do not have the Earth Impedance facility built in, but you can get stand alone units for about €100,00.

Recommend this book: https://www.amazon.co.uk/Linstallat...p-2416000055/dp/2416000055/ref=dp_ob_image_bk for all things French electric's.
 

Reply to Line to Neutral 0 volts , live earth 30 volts , neutral live 30 volts in the Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
2K
Just interested in peoples thinking on using the neutral through the earthing system like I came across today. I've come across many wrong...
Replies
10
Views
2K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
968
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
414
Did a check on a ring circuit, due to board having to remain live I did it at a socket.. Was an RCBO, had checked RCD side and all tested ok...
Replies
3
Views
892
Advertise Here

New Posts (Please Reply)

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Top