Hi Guys

Go easy, I'm learning.

Went to look at a little job today. In brief TNS, split 25mm tails. First CU is next to service head with 16mm Earth. 2nd CU is about 5m away in new extension with 16mm Earth.
First CU is bonded to Gas with 6mm, and the 2nd CU is bonded to water with 10mm.

I was a little confused, as I understood that both CU's had to be bonded, or if i upgrade the 6mm to gas, does this cover regs.

Although the customer didnt have the certs, he had this signed off late last year.

All the guy wants is a small radial from the extension consumer unit, so I just wanted t clarify.

And is it correct, that I would only need to do Installation Cert for that additional circuit.

Thanks in advance


Dave
 
Hi Dave, Apply the adiabatic equation to your 6mm[SUP]2[/SUP] Gas main protective bonding conductor, it may well comply. If it complies BS7671, all well and good there would be no need to upgrade it. If you use the adiabatic equation for compliance, make sure your calculation and statement of compliance are included in your EIC. If not replace your Gas main protective bonding conductor with 10mm[SUP]2[/SUP].
Yes, you only have to do an EIC with a full set of test results for the final circuit you install. However, it is considered good practice to identify the other final circuits of the installation on the Schedule of Test Results, but you are not required to include any test results for the other circuits. This approach would aid clarity in your case where the bonding is split between two DB earth-bars rather than from a single MET.
 
Last edited by a moderator:
I may stand corrected but bonding conductors are sized by selection...not the adiabatic equation....(543.1.1).
As PME conditions do not apply main bonding conductors must be not less than half the cross sectional area required for the earthing conductor,and not less than 6.0mm. (544.1.1).
Main bonding should really go to the MET at the intake,however as bonding is present...(and within the minimum 6.0mm)...and as long as there are no signs of any problems,you have no worries if you are only carrying out an alteration or addition,just note on the cert any deviations from 7671,but that those deviations do not compromise the safety of the installation.
 
In TT and TNS there will be very little current flow within the bonding conductors, 6mm is is there pretty much for mechanical strength. As for sizing, Wirepuller's excellent post is spot on.

If the second CU is fed from the first via a 16mm cpc then that may well be suitable as a combined cpc/bonding conductor, this will allow extraneous conductive parts to be connected at that CU.

Its not a case as such that both CU's need bonding just that all extraneous conductive parts need to be connected to your met.

Keeping your bonding localised, keeps the touch voltages down. Though it would be no real issue if all bonding was carried out at the first CU.

Regards Chris
 
As Chris has stated you only need one bonding cable from each of the main services (Gas/Water) to the installations MET or EMT, but NO need for both as they are already linked via the 16mm tail from the MET!! So if you have a 6mm and a 10mm bonding cable from the main water service point, you can safely remove the 6mm leaving the 10mm in place serving the installation. The second CU should be classed as a sub-main and it's earthing bar classed as the installations EMT!!

Unknown Parellel earth paths are difficult enough, without adding to them.
 

Reply to Little confused about Earthing - Some advice Please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
771
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Need help with a quote here. I’m wanting some sound advice. Was called out to the hot water not working so repaired the issue within the panel...
Replies
10
Views
1K
Just double checking please - in situations where the main earthing conductor csa is calculated, and in a TNS installation, the 50% bonding...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock