J
Jon Marr
Hi Guys, we are currently trying to locate several SWA cables in and around our carparks. I have bought a Fluke 2042 cable Generator and Locator but am struggling a bit.
The Gen has 2 ports on the top, can anyone advise on where we connect these to the exposed (dead) SWA? We think there may be a break in the cable so currently getting a >500 with our 1652 on insulation resistance. Does the cable need to be complete (joined at one end) to work or can we do it as is?
Also the generator has 3 strengths, any idea which is best?
Thanks again.
Also on a second note (Apologies it has been a few years since I finished college), when performing a IR test on the cables, at 250v it gives us >200 straight away. But when at 500v is starts off around >120 and slowly climbs to >500, why is this (Fluke 1652C)
Kind regards
Connect the + terminal to a core of the non powered cable (or the armour) and set the transmission level to high if the cable is properly buried.
Use the receiver at the start of the circuit and select the sensitivity somewhat higher than that required to detect the accessible cable, as you move away you should be able to trace the cable location, if there is a break in the core you are connected to then the signal should be lost at that point. Then try again from the other end and if the point of signal loss matches there is the break.
Reply to Locating with a Fluke 2042 in the Electrical Tools and Products area at ElectriciansForums.net
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
4K
When putting in some duct for fibre broadband we also put in a few lengths of 63/50mm twinwall duct "just in case" we needed that, as we knew of a...
For emergency use, when there's a power outage, the current situation (no pun intended) is that I'm running a hook up cable from the 16A socket on...
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...