SirKit Breaker

I have a job coming up to replace existing batten fitting in loft with a 6ft Flourescent tube, no problems there, not altering anything, its on the existing house lighting circuit protected by a 5a rewireabe fuse. Zs and IR of circuit well within spec.

Customer wants 6 off twin switched sockets in loft all surface mount to floor to power his model railway set up, max demand on circuit of about 4 amps on a bad day, he only wants so many so as to not have extension leads all over the floor. He doesnt want any decorating or mess if avoidable in the house.

The CU is Wylex with 8 rewireable fuses, Ze and all the other basics etc are all Ok on a TNC-S supply.

In the airing cupboard in the bathroom there is a disused 2.5mm T&E cable which is fed from a 15a rewireable fuse (old immersion heater supply), I have tested the cable and it is fine IR of 233meg, Zs cant remember but it is well in spec. This cable is not accesible between CU and Airing cupboard. The CU is at ceiling height in cupboard which is conveniently directly below the Airing cupboard. The cable is only exposed for the 4 or 5 feet it is clipped to the door frame.

I intend to reuse this cable, but put it in plastic trunking. Then extend the cable into the loft as a radial. Total length of circuit from CU to last socket is about 8 metres.

At the point where i extend i am going to fit a shower CU in the airing cupboard, with 40a 30ma RCD incommer and a 60898 16a MCB.

Am i missing anything, is it compliant? Comments and opinions please good or bad.

I will also replace the rewireable fuse with a plug in 15a 60898 MCB just for convenience. There are plans for a CU upgrade but not until funds allow.

Cheers...........Howard;)
 
hi mate just reading youre thread,everything sounds good but just not with you on the 40a 30mA incomer when only being fed from a 15A breaker(obviousley sockets need to be rcd protected) but is there not a suitable rcbo to feed the sockets????? Although would 4mm cable need to be used if just a radial:confused::confused::confused:
 
I would say that this is probably because shower units tend to come with a 40A double pole RCBO, it is often easier and cheaper to use this as the RCD protection and put a smaller breaker in for the MCB protection.
 
Can't see a problem with that myself but an rcd fused spur may be a better option, put the spur in the cupboard where the cable ends then up to the loft to your sockets;)
 
Although would 4mm cable need to be used if just a radial:confused::confused::confused:

No need for 4mm cable if the current carrying capacity of 2.5mm after correction factors can take 15 amps. In a domestic, I doubt you'd find enough correction to warrant a 4mm radial on a 15A, but who knows!
 
Can't see a problem with that myself but an rcd fused spur may be a better option, put the spur in the cupboard where the cable ends then up to the loft to your sockets;)

Good idea, why didnt i think of that! Just goes to show know matter what you know, or how long you have been doing it there will always be an easier way.

Cheers....................Howard
 

Reply to Loft Sockets. in the Australia area at ElectriciansForums.net

Similar Threads

Hi fitting a a couple loft sockets on a radial circuit. I only have 2.5mm cable and really don’t want to buy a reel 4mm2 is it ok to use on 32A...
Replies
10
Views
2K
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
773
Afternoon all, I have an issue with the loft socket. When we moved the previous owners had a 2.5mm cable going up from the CU Via FCU however...
Replies
7
Views
1K
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
776
We have had builders in, who have stopped for Xmas. My daughter tried to do a wash. The wash machine wouldnt. Its power socket is dead. I...
Replies
4
Views
617

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock