Hi, Part P newcomer here. When taking for example a loop impedence reading on say a ring main, linking live/neutral together you divide the result by 2 to give a reading for each cable because they are the same csa2 but how do you caculate for a live/earth reading when the cpc is a different size? Also information on how to do an insulation test on SELVs or flourescent lighting circuit without linking evey fiitting out?:)
 
Yes sorry I meant a continuity test when cpc is different size to live conductor but the lighting circuit question remains the same.
Carl.
 
Hi, Part P newcomer here. When taking for example a loop impedence reading on say a ring main, linking live/neutral together you divide the result by 2 to give a reading for each cable because they are the same csa2 but how do you caculate for a live/earth reading when the cpc is a different size? Also information on how to do an insulation test on SELVs or flourescent lighting circuit without linking evey fiitting out?:)

for the ring

like Ian said, its continuity you are looking for

do end to ends

r1 (line)
rn (neutral)
r2 (cpc)

link incoming line to outgoing neutral and vice versa

reading between line and neutral at sockets is r1+rn divided by 4

link incoming line to outgoing cpc and vice versa

assuming 2.5/1,5 tw&E,

2.5 divided by 1.5 = 1.66, so r2 value should be 1.66 times higher than r1 and rn value

you should read r1 + r2 divided by 4 at the sockets, highest reading is your (R1+R2) for the ring (normally at a spur)

your readings should be +/- 50 milliohms for each socket
 
Last edited by a moderator:

Reply to loop readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
595
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
977
Hi all, I've just tried wiring an indesit IB65B60 induction hob. I read the instruction manual and it said for 240v connections to put the...
Replies
23
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock