Hi,

So I did and insulation resistance test on a lighting circuit today.

L-N 0.23
L-E 34.9
N-E 35.8

The L-N is under the required reading, what do I do?
Do I turn it off completely or advice the customer to get it re wired and leave it on???? Cheers
 
Sure you are not getting a short from a lamp or something daft like that?

If not then you need to find the part of the cct with the problem.
Split the cct down and test parts until you find the issue.
 
Are you sure there isn't a dimmer in the circuit?

You can't make a customer switch a circuit off only recommend. I doubt all of it needs a re wire, any outside lights on this circuit?

Is this something you've installed? Or just an eicr?
 
no dimmers, there are outside lights but lamps out. I haven't installed anything - the lamps keep blowing so was testing to try and solve a problem.

- - - Updated - - -

theres no neons or dimmers in the circuit
 
Daylight sensor/pir motion sensor switch maybe? I wouldn't advise on a re-wire or any other remedial action until you know exactly where the fault is, you may end up with egg on your face.
 
Hi,

So I did and insulation resistance test on a lighting circuit today.

L-N 0.23
L-E 34.9
N-E 35.8

The L-N is under the required reading, what do I do?
Do I turn it off completely or advice the customer to get it re wired and leave it on???? Cheers

Are you actually an electrician? You can't ask a forum whether a rewire is required!
 
Jpaul, are your test results in ohms or Mohms?!

What test voltage is being used?

On a lighting circuit I'd be looking at the usual culprits first. PIR, dimmer, extractor fan, shaver socket etc
 

Reply to low insulation resistance reading in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
522
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
978
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
605
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
834
Hi all, I have an unusual issue with a recent rewire I have just completed which I hope you guys can assist with. For background, this is a...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock