Discuss low IR N-E in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
S
sivoodoo
Hi all,
Just done a quick test on a ring for a friend, the results are as follows.
Continuity tests are all fine.
Insulation Resistance:
Line - Neutral = >299 MΩ
Line - CPC = >299 MΩ
Neutral - CPC 39.6 MΩ
Where should I begin in finding the problem with the N-E low IR.:confused:
Thank you.
Yes disconected at board.
Removed both legs of ring at board and tested L- E, L-N, N-E.
quick responses thank you guys.
here are the continuity results:
r1 = 0.44
r2 = 1.35
rn = 0.55
(R1+R2) at all socket outlets were between 0.38 (min) to 0.46(max)
you say its ok but r1 and rn have different readings its a ring so they should be the same r2 should be higher (assuming 2.5 t&e installation) due to higher resistance, code 3 im afraid further investigation required
yup just realised that r1 and rn are 0.1Ω difference and as far as I can remember isnt the maximum supposed to be a difference of only 0.05Ω
Yup further investigation required.
What could be a cause of this, a screw catching the neutral someplace?
could be mice chewing on cables for all i know (sorry but with out seeing it pretty hard from where im sat to say thats yours problem)
but what i would check first is all appliances un plugged, neons turned off, isolated all spurs (test later if needed) etc then re test. if that dont work split ring (think of it as two radials) and re test. in theory one radial will be faulty one will be ok. keep splitting 'faulty radial' till you find the 1. previously un noticed fuse spur with neon and dodgy connections! or 2. bad leg of cable that the mice have been eating!!!!!!
have fun!
makes a change from the apprentices though god they get really hungry some times i have to feed them sometimes once a week!
Thanks Plan, and welcome to the forum!
I shall be going back in a couple of days to have a play around, the house is empty so I can take my time, thanks for the advice.
Dont know what attracts them to cables ! pvc ? emf ? knowing their being a pain in the rear ? (your not feeding me ir'll stop your cooker !)
They are nearly as adorable as cheeky unobservant lazy apprentices, but as all sparks know these apprentices are a urban myth!!!!!!
No idea why they go for them warmth from overload boredum dares from their mice friends
They gnaw at anything they can get hold of to sharpen their teeth.
Back on topic, i have in the past had clear IR results only to find that cables had been chewed.
A little test for you to try is to cut off a length of say 2.5 and put 500V on it.
Then strip away chunks of insulation down to the copper so that its well damaged and test again.
See what the result is!
had a similar problem on a pir recently, r1 and rn ok tho, thats probably a loose connection, had a lower ir on n-e but well within spec so didnt pay too much heed, untill i connected the new rcd cu, then the ring circuit tripped, remeasured and found short n-e which was not apparent at first test, so socket plates off, break ring and retest ir in sections, during this found a small nick in neg insulation, which i repaired, problem solved. the nick was so positioned as to be out of sight at first glance and was bearing against the backbox in varying amount when socket plate tightened, trapped neg to plate screw would give same fault, the act of plugging in and unplugging could vary the ir or even give an intermitttent short. really bad news is ,couldnt really charge the client for all the faffing about to find it,
Cheers everyone the client wants a rewire now, yipee. That saves a whole load of crawling about for (no swearing) all!
Reply to low IR N-E in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...