robo83

-
Reaction score
40
Testing a ring final circuit today. R1+R2 is fine, same as end to end r1 rn and r2.

However IR test is coming back 1.87M ohm. I split the circuit and located a section (one side of the ring is clear >999).

The customer doesn't want any walls or ceiling touched. As this is greater than 1M ohm can this be left and simply noted on cert.
 
are you doing a EICR? if so, then you just record what is there. it's a report . it's then up to the customer, considering your advice as an expert, to decide what to do about it. your remit does not cover fixing anything. you're just providing a report.
 

Reply to Low IR ring final circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock