Testing a ring final circuit today. R1+R2 is fine, same as end to end r1 rn and r2.
However IR test is coming back 1.87M ohm. I split the circuit and located a section (one side of the ring is clear >999).
The customer doesn't want any walls or ceiling touched. As this is greater than 1M ohm can this be left and simply noted on cert.