Hi guys need help to stop me me from having no hair left. Been pulling it out for 2 days. Routine inspection RCD not tripping. But further checks show the voltage I'd too low. Old lead cable supply Ze 0.22 Only getting 1A fault current and voltage 193 volts to earth. Any ideas?
 
Hi guys need help to stop me me from having no hair left. Been pulling it out for 2 days. Routine inspection RCD not tripping. But further checks show the voltage I'd too low. Old lead cable supply Ze 0.22 Only getting 1A fault current and voltage 193 volts to earth. Any ideas?
Is the voltage within the ranges specified
 
Ze = 0.22 what? Ohms? Kilohms?
If it's 0.22 ohms, then the results don't match up which means one of the tests didn't work out. If it's kilohms then it might be correct, 230V / 220 ohms = approx 1A PEFC. Not very good earthing but not an error. The voltage reading depends on the effective input resistance of the tester... which test gave the 193V reading?
 
Ze = 0.22 what? Ohms? Kilohms?
If it's 0.22 ohms, then the results don't match up which means one of the test didn't work out. If it's kilohms then it might be correct, 230V / 220 ohms = approx 1A PEFC. Not very good earthing but not an error. The voltage reading depends on the effective input resistance of the tester... which test gave the 193V reading?
Put the question better than I could Lucien, nice one
 
If the supply really is down at 193V is it just possible the RCD electronics are unable to fire, but it would worry me and I suspect it is faulty. Basically I doubt anyone would make an RCD that was sooo... sensitive to low supply volts.

If you have an earth rod / TT setup then 220 ohms is just above what the reg say is "stable" but well below what is needed to trip most RCD. For 30mA / 100mA for sure, regs say 167 ohms for 300mA so touch voltage below 50V, but obviously 1A PFC would fire it if working!

But if the earth is using the lead sheath it ought to be a TN setup and then it is badly wrong!

Finally the low volts is a worry (if your meter is right, which it probably is). As asked above, what is the L-N volts? If they are 230V-ish then something is pulling the "earth" up noticeable. A fault on this load? Was it tested with all breakers open? Or a fault on someone else's system sharing this supply?

Any pictures, more info?
 
I had a similar reading last week.

Simple job: disconnect a socket from a shed, remove old shed, build new shed, reconnect socket in new shed. A quick Zs test when finished to make sure all's well, but I'm getting >1999 ohms? Test voltage and I get ~240V L-N, ~210V L-E, and ~45V N-E. Turn off the breaker, test for dead, still getting ~45V N-E?

Okay, off to the board, Ze test >1999ohms. Open meter cupboard:P9161075.JPG:
 

Reply to low voltage to earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
982
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
977
Hi everyone I asked my assessor about touch voltage and he was not keen on explaining properly and gave me a rough answer which made me think...
Replies
32
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock