D

dannyv

Can anyone tell me how low the Ir value would be n/e for a rcd not to hold in! Would like to know as I always get problems prior to changing fuseboards
 
ohms law. 7.6kohms or 0.0076Mohms.

this is assuming that the voltage is 230v and that the RCD will trip at exactly 30ma.

Both of the above statements cannot be guaranteed

Edit: i totally agree with wirepuller, if i gets anywhere near 1Mohm, then invesitgate further.
 
Last edited:
It would depend completely on the sensitivity of the device.

As wirepuller says, it is irrelevant as BS7671 2008 states >1Mohm, although (in the words of Tony Cable) that is simply an exam question and anything near that would require investigation. The answer would definately not be an IR value, and would be more of a low reading ohmeter value.
 
What's the best quickest test to do on a fuseboard change survey to see if you ll get rcd trip problems neutral to earth across the whole install ?
 
Stick a earth leakage clamp meter around the tails and this will give you a start.

High leakage try taking the fuses out one at a time but this only gives you live earth leakage as the neutrals are all in one bar. So if high leakage still there taking neutrals out one at a time to find cct but this if hassel on a tight 3036 board or any board crammed with cable.

Make sure loads are disconnected unplugg in case of faulty appliance.
 
What's the best quickest test to do on a fuseboard change survey to see if you ll get rcd trip problems neutral to earth across the whole install ?

Method 2 IR test.
 
There's only one way...do an IR test.... anything under 1mohm will need investigation.
Also check for borrowed neutrals...most likely on the landing light of a 60's built house.
 

Reply to Lowest n/e Ir value for a rcd to trip does anyone know? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Long shot but thought I’d try, have a lighting circuit that trips the RCD as soon as the neutral touches the neutral bar for said RCD. Bypass that...
Replies
6
Views
2K
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K
Hi Basically I have visited a youtube link of another electrician and he is talking about how many electricians find RCD fault very hard to...
Replies
24
Views
3K
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms...
Replies
58
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock